Water heater expansion tank.
James Day_2
Member Posts: 191
What is the proper way to charge a expansion tank on a indirect water heater.
Thanks James
Thanks James
0
Comments
-
Follow the manufacturers instructions...
and if my memory serves me correctly, it states that the diaphragm should be charged to the same pressure as the minimum operating pressure of the system, with ZERO water pressure on the tank. In other words, charge the diaphragm BEFORE you install it.
This way, any pressures generated by the expanding water will be absorbed by the tank and keep the pressure well below the relief valve setting.
METhere was an error rendering this rich post.
0 -
I should probably read the instructions.
James, I have been charging them to 60 PSI for city water and 40 for well water. We have highly fluctuating water pressure here in the few areas with city water. We have found that we stay out of trouble at 60 PSI.
I think I will re-read the instructions on one.0 -
Did any one ask...
... if the expansion tank is on the boiler side of the indirect, or on the domestic side?0 -
expansion tank
Its on the domestic side0 -
doesn't matter - domestic or heating
If you follow manufacturers instructions (like ME said above) then it wouldn't matter.
Set at minimum operating - then you have the correct amount of expansion room in the exp. tank.
If you did it like MEPlumber (for domestic) - that would work most of the time, but maybe not always - if the operating pressure were higher than 60# - less expansion room - relief valve go poppy or weepy, weepy, weepy every hot/cold cycle.
Big issue.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements