Rule of thumbs

j a_2
Member Posts: 1,804
I am not a huge fan of rules of thumb to finalize a question...However just to confirm my understanding, can it be said in ONE pipe steam, counter or parell flow, if you have an existing 2 inch main then your replacement boiler should not be bigger than 387 sq. ft. of steam...Does that make sense? thanks J A
0
Comments
-
Well,
that would be the normal limit for a 2" main. in that system.Retired and loving it.0 -
And as Dan will agree I am sure
Just because that is the limit on the size it does not mean that the system is that size. I have seem systems put in by dead men that the main was undersized from day one. Low bidders got jobs back in the day too.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0