Need Modulating Vaporstat
Steve Garson_2
Member Posts: 712
Is there such a thing? Just upgraded a Smith 19A-6 with a new Powerflame CR1-G-12.
The problem: the system runs on 6 ounces and I learned the pressuretrol that controls the modulation doesn't go low enough to function. As a result, I can't modulate the burner.
Does anyone know of a control with a 120 ohm potentiometer that will allow me to modulate a low pressure system like this?
Steve Garson
Boston, MA
The problem: the system runs on 6 ounces and I learned the pressuretrol that controls the modulation doesn't go low enough to function. As a result, I can't modulate the burner.
Does anyone know of a control with a 120 ohm potentiometer that will allow me to modulate a low pressure system like this?
Steve Garson
Boston, MA
Steve from Denver, CO
0
Comments
-
below 6 oz.
can you replace the pressuretrol with a vaporstat. i think some of these modulating systems use 2 vaporstats-one to handle the transition from high flame to low, and the 2nd to cut the burner off completely if the pressure continues to rise even on low fire.
the 0-16 oz honeywell vaporstats would be right for you. --nbc0 -
Available.... YES....But
you have to combine a few components. If you start with an electronic modulating pressure control that accepts a typical 4-20 MA pressure sensor signal, you can simply swap in a pressure sensor that operates in a lower range. The lowest most controls some with is 0 to 30 psi, however, you can get sensors that operate at much lower ranges, say 0 to 15 ounces. The display will not be correct , but operation is uneffected. You would then just need to set up the operating range off a reliable vapor gage. Omega, ashcroft and others have pressure transducers.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements