hot water loop off steam boiler
STEAM DOCTOR
Member Posts: 2,199
Good morning. I am running a hot water loop off a steam boiler using the tankless coil. Do I need to mix cooler water into the loop to prevent the water from flashing to steam or is the fact that the water is pressurised and hence a higher boiling point enough to prevent the water from flashing to steam. Thanks in advance for the advice.
0
Comments
-
Yes and no
The water will not boil due to the pressure, however you are required by code to use a mixing valve in order to prevent scalding and it also allows the hot water to stay a consistent temperature. Just think of how hot the domestic hot water can become while the boiler is making steam, 170-180F perhaps?
You may also want to consider adding a flow regulator. I have been thinking about adding one to my setup because if we try to get too much hot water it cools down a lot due to the volume running through the coil.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
hot water
I am not running domestic hot water off the loop. The loop is a heat only loop.0 -
Space heat or DHW???
Copper or plastic distribution?
Gots to know...
METhere was an error rendering this rich post.
0 -
my mistake
Ah, I thought when running hot water for heat you simply pull water from below the steam line. Did not know anyone ever used a loop for that?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Got it...
If you are running plastic for distribution, you will want to protect the tubing from higher operating temperatures. If it is copper or iron, not a problem provided you can maintain at least 5 PSI on the top of the system (.434 PSI per vertical foot above the boiler, PLUS 5 PSI).
If it were DHW, you'd have to use an antiscald mixing valve. I'd suggest using the same thing if you are dealing with plastic.
METhere was an error rendering this rich post.
0 -
hot water zone
dans book, the golden rules of hydronic heating.page 77.you will find a piping diagram to make it easy for yourself.0 -
-
Heat loop off a coil
How many BTU's are you going to put on this loop?0 -
copper
There is copper piping. The highest point on the zone is aprox 30' high so I cant come off bottom of boiler.0 -
I would....
...at least put some form of mixing valve, either manual or automatic mixing in the loop's return water. Try to maintain 180 on the loop while the boiler is fully steamed. The worst that happens is you wind up not using the valve; and you get a little more control of the system.0 -
hot water loop
You also need a circ pump, expansion tank, aquastat and B&G FB-38 fast fill valve, and a back flow preventor. You have to treat this loop just like you would any hot water boiler loop(zone).0 -
hot water loop
one more thing I forgot to add, throw on a Taco SR501 single zone switching relay.0 -
flow chat
This is a question.
On the out part of the tankless coil, you connect a expansion tank, then circulator, then flow check valve, then pressure reducing valve?
Then the return goes back into the IN part of the tankless coil, with a flow valve?
Water supply gets tapped into the in part of the tankless coile after the flow valve?0 -
flow chart
i meant the title for the post above to be flow chart0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements