indirect water heater
ashman
Member Posts: 1
7 years ago I installed radiant flooring in my new house powered by a Munchkin.
Against my professional's advise I installed an indirect water cylinder.
Winter is great except since I zoned with circulators the tank gets
over-hot when the other zones are calling for heat. I think the primary
pump flow just pulls a low flow through the tank.
In the summer the Munchkin does it's thing and even though it's a modulating boiler it seems like an over kill.
The Crown indirect has years of life left so is there any way I can convert it to another heat source/form?
The winter flow problem could be fixed I think by replacing the
secondary pump with a zone valve. Any one got a better idea? If that is the only solution what
valve is ideal?
Against my professional's advise I installed an indirect water cylinder.
Winter is great except since I zoned with circulators the tank gets
over-hot when the other zones are calling for heat. I think the primary
pump flow just pulls a low flow through the tank.
In the summer the Munchkin does it's thing and even though it's a modulating boiler it seems like an over kill.
The Crown indirect has years of life left so is there any way I can convert it to another heat source/form?
The winter flow problem could be fixed I think by replacing the
secondary pump with a zone valve. Any one got a better idea? If that is the only solution what
valve is ideal?
0
Comments
-
I have the same set up
in my basement except that I zone with zone valves. If your installer did his piping according to the installation instructions, you should not be experiencing gravity flow which seems to be over heating your indirect.
Here are the installation instructions:
http://www.munchkinboiler.net/uploads/MunchkinRevision2Installation.pdf
I'm sure your professional did a great job - he might just be missing a check valve or two.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
or
It could be that a flow check is sticking open. The other question I have is do you have a mixing valve on your indirect?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements