Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Steam duct coil

Jason_13
Jason_13 Member Posts: 304
I was wondering how to determine the capacity of a steam duct coil to determine boiler replacement.

I have a duct coil which measures 12 x 18 2 pass. This is installed in a vapor system which I thought a little unusual. 

The existing boiler is grossly over sized as they have 4 burners blocked off.

Any help would be greatly appreciated.

Comments

  • Steamhead
    Steamhead Member Posts: 17,314
    If there's no better information

    go by the size of the steam pipe feeding the coil. For example, an 1-1/2" pipe could serve up to 168 square feet. 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • MikeyB
    MikeyB Member Posts: 696
    Indirect Heating

    Go to Resources at the top of the page, then click on Tech Stuff, then Hot Tech Tips the click How Indirect Heating Works,
This discussion has been closed.