Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Industrial Combustion DEG
boiler_man
Member Posts: 21
in Oil Heating
I did some routine maintenance on this IC burner burning no.6 oil. I changed the nozzle all is well going from low fire to high fire, but when going back down to low fire unless it in manual and being adjusted very slowly the flame will extinguish and burner goes into safety. Anybody have any idea what is going on here?
0
Comments
-
6 oil
What temperature is the oil? Was the gph same for same between nozzles? It sounds too lean; it will light off with the excess air with the gas pilot, but on the way down to low without the pilot there it snuffs itself out.0 -
Any update?
Just wondering if issues were cleared up with this burner? Lots of views, and no replies.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements