Too Small or Too Big
Murph2
Member Posts: 1
my 28 year old Wild-Mclain steam boiler is leaking (Oil Fired).I am converting to gas.Both contractors given to me by gas company walked around the house and measued. One sez I need a 4 section boiler the other sez I need a 5 section boiler.Now my wife (retired math teacher) and I (retired phone co.) Found a chart on line and did our own measuring. We came up with a 4 section,but if you add the pipping lost factor of 1.33 we come up with a 5section requirement.We have 10 radiators . house built in 1927. Half col. radiators and half tube type.Steam main is covered for the length of the house and the pipes coming off the top of the old boiler were covered with insulation.28 years ago the oil company took out coal to oil boiler ad installed an oil fired steam Weil-Mclain model p-466E 144000DOE,450 sq ft of steam.Ran great all radiators in the house got hot almost at the same time Using Gorton valves thru out.So now we are getting a Burnham gas fired steam boiler. One cotractor measured 229 sq ft of steam. the other guy who I like is measuring oer 300 something sq ft. The over 300 sq ft uy is adding a loss factor of the pipes so he sez.it is hard to ID the ra. diators and apply a chart to do our own cal.My question is how do we determine who is right or who is maybe to conservative or to over the top. Your ideas would be appreciated. i wish I had read your book 30 years ago.Thanks murph
0
Comments
-
That's a pretty big spread.
If you post a couple pictures of the 2 kinds of radiators you have, we could help you identify them, and possibly direct you to the area of the library here, that contains the charts you need. While you have the camera out, take a couple shots of the boiler. Show the pipes up in the ceiling and the ones near the floor.
What city or state are you in? Have you tried to get a 3rd contractor in there yet?
I am not 100% sure, but I thought that the pickup factor of 1.33 is allready built in to the boiler. I thought that it should be as simple as measure the square feet of the radiators and match that number to the square feet of the boiler. If you add 1.33 to your radiator EDR you will have a boiler 1.33 too big.0 -
Pipes insulated?
I agree 100% with what crash said, you can just size the boiler by matching the IBR boiler radiation with the connected radiation (in sq ft of steam). I would add that the steam pipe coming out of the boiler, and all the steam pipes in the basement, should be insulated with a minimum of 1" pipe insulation. that will make the basement get chilly but make the fuel bill go down and the boiler will work much better. The insulation is not cheap but you can do it yourself and save the labor cost.
Please post some pictures so we can see if anything else has to be corrected while they replace the boiler.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Boiler Replacement
It looks like your approaching the boiler replacement the right way by doing your homework first. As others have mentioned, post some pictures of your boiler. Take them from several angles and include the piping connected to the boiler in the pictures so we can trace the piping. (We can blow them up if we need more detail.) Having the near boiler piping properly configured is extremely important to success operation of the your steam system. Here are some links below that may be of use to you.
Have a great 4th!
- Rod
Links:
Steam Heating Primer
http://www.heatinghelp.com/article/11/Hot-Tech-Tips/128/A-Steam-Heating-Primer
Replacing a Steam Boiler 1
http://www.heatinghelp.com/article/11/Hot-Tech-Tips/186/How-to-replace-an-old-steam-heating-boiler
Replacing a Steam Boiler 2
http://www.heatinghelp.com/article/236/For-Homeowners/1490/How-to-have-a-boiler-replaced-without-getting-steamed
Importance of Insulating Steam pipes
http://www.heatinghelp.com/article/11/Hot-Tech-Tips/300/Why-you-should-insulate-steam-pipes
Video on Importance of Near Boiler Piping
http://www.heatinghelp.com/article/107/Steam-Heating/118/Steam-boiler-near-boiler-piping
Boiler Ratings Explained
http://www.heatinghelp.com/article/11/Hot-Tech-Tips/143/Boiler-Ratings-Explained
History of Boiler Sizing (Why you need to calculate your systems boiler size)
http://www.heatinghelp.com/article/11/Hot-Tech-Tips/180/How-that-steam-boiler-got-to-be-so-big0 -
SQ FT EDR RATINGS
Crash, you are absolutely correct.
The EDR or SQ FT rating on the boiler already has the pickup factor included. The rating is intended to be matched to the actual radiation of the system. Usual practice on a system with insulated pipes of normal sizes and lengths for a system of its size, is to select the boiler with the nearest rating that is larger than the actual radiation of the system.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Boiler Swap
While that is a big spread, bear in mind that square footage of steam multiplied by 240 = BTU, so you are still in the range of a 3 section, even with adding for piping loss. Are these guys well versed in steam? Dont go with anyone who isnt. If you are curious about their eval, call and ask them why they did what they did.
Also, look on line for steam radiator sizing. There are charts available that should help you in your sizing efforts.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements