Wet Steam From One boiler

quark555
quark555 Member Posts: 3
Hi,

At work we have two boilers (Cleaver Brooks) and they have one common header and same feed water tank. One boiler is giving wet steam when it is running while the other is working perfectly. Both have the same settings, and they were just services recently. Any help plz.

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    one wet boiler

    could one be running at a higher pressure than the other?--nbc
  • quark555
    quark555 Member Posts: 3
    edited June 2011
    Usually not running at the same time.

    Hi,

    Usually they are not running at the same time. (we run them altrenatly every other day).
  • Al Letellier_21
    Al Letellier_21 Member Posts: 402
    wet steam

    Dirty water can cause wet steam. Have you skimmed the boiler of late. Even crystal clear water in the glass doesn't mean its clean. Do you see water droplets in the glass when the "wet" boiler is running? If so, its got dirty water. Skim it;
  • quark555
    quark555 Member Posts: 3
    No Water Droplets

    Thank you for your replies. Actually I can not see any water droplets. Do you think any other reasons can lead to the same problem?
  • Rod
    Rod Posts: 2,067
    Wet Steam

    Hi- When the boilers were serviced, was there any changes, like piping, done on the boiler now producing wet steam??  Check that boiler for obvious things like higher pressure, water levels etc.   Have you tried boiling a sample?  What is your indication that it is producing "wet steam" ?