boiler sizing
STEAM DOCTOR
Member Posts: 2,156
I was recently hired to do a consultation on an old house renovation. The homeowner doesn't trust the people that the general contractor is bringing in and I am getting the impression that the GC also doesn't trust the people that he is bringing in. They are replacing the old massively over sized oil boiler with a new gas boiler. They only want to go with burnham because the local gas company gives a rebate for on the burnhams. I did an EDR survey and came out with 148 mbtuh. I told them to go with the IN6 which is rated for 144mbtuh. The problem with the IN6 is that the manual only requires one 2" riser from the boiler. My gut tells me that this is to small. There is no way that I will be able to get the boiler installer to exceed the manufactures recommendations.I am wondering if it is worthwhile to tell the installer to use the IN7 which on one hand would be over sized but on the other hand would require him to use two 2" boiler risers as per manufacturers recommendation. Thanks in advance for the advice and input.
0
Comments
-
BTU net, gross, or input??
The ratings always cause confusion.
When you did the survey, what was the total sq ft? I am guessing that it was about 617, and thus your number of 148,000 NET BTU. sq ft x 240btu.
If this is correct, then you need to be sizing according to sq ft, or net btu steam. In which case you would need an IN8.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
gross
Sorry bout that. The btu's are the gross output. The edr is aprox 465(465x240=111600x1.33=148428)0 -
IN6 is correct
Ok, you got the right model, and if the manufacturer says it is acceptable to pipe it with one 2" riser, then it should be fine, as long as all of the other little details are correct.
I note that the IN12 has 2-2" risers and it is more than twice the capacity than the IN-6, therefore the velocity in the risers will be even greater than that IN-6 with one riser.
It is very important that all other details of the piping is exactly correct in order to deliver dry steam. No reductions in the horizontal piping, make sure the swing joint / double 90 is present coming off of the riser, etc.
YOu should be OKDave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
exit velocity
The IN6 has a steam velocity of 42.85 feet per second. The IN7 with the two boiler risers has a steam velocity of 25.7 feet per second. The IN7 also calls for a 3" header as opposed to the IN6 which only calls for a 2" header. My gut would tell me that even though the IN7 is approximately 25mbtu over sized it would still do a better job in heating the home at lower cost.0 -
The IN6 is rated 450 square feet EDR
while that's not much less than your 465 square feet, I think I'd go with the IN7 and down-fire it a bit. You won't be working the cast-iron so hard- remember, an atmospheric boiler has all the cast-iron above the flame rather than surrounding the flame as on a power-burner unit. So the heat is pretty concentrated in a small area.
And the minimum specs would force them to install a better header.
Make sure the installer tests the boiler with a digital combustion analyzer before you finish paying them!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements