Hi all,
Got a York M# FC48C3XN1A, S# A0C7571528 A-Coil on aYork M# GY9S080C16UP11J, S# WOC6096611 gas furnace. York filter rack on the side with Air Bear 20 X 25 filter in it.
This year the condensate is "overflowing"? even though it is draining. I installed an EZ-Trap, but the problem has come back. It seems to be after a long cooling cycle, the ac is 2 degrees off setpoint.
Any ideas? When I installed the trap, I also inspected the coil and pan, clean. Went ahead and sprayed coil with self-rinsing coil cleaner.
This is our unit. Boss said didn't do that last year. (I wasn't working for him then). Only thing that has changed from last year that I know about is the new stat I installed 3 months ago.
Any ideas? When we looked at it this afternoon it was draining fine, but making gurgling noises, which alerted us to the problem.
Thanks Don in MO
Got a York M# FC48C3XN1A, S# A0C7571528 A-Coil on aYork M# GY9S080C16UP11J, S# WOC6096611 gas furnace. York filter rack on the side with Air Bear 20 X 25 filter in it.
This year the condensate is "overflowing"? even though it is draining. I installed an EZ-Trap, but the problem has come back. It seems to be after a long cooling cycle, the ac is 2 degrees off setpoint.
Any ideas? When I installed the trap, I also inspected the coil and pan, clean. Went ahead and sprayed coil with self-rinsing coil cleaner.
This is our unit. Boss said didn't do that last year. (I wasn't working for him then). Only thing that has changed from last year that I know about is the new stat I installed 3 months ago.
Any ideas? When we looked at it this afternoon it was draining fine, but making gurgling noises, which alerted us to the problem.
Thanks Don in MO
0
Comments
-
Water
Hi Don! How long is the drain line after the trap?If long,is there an air vent after the trap?How old is the system? A lot of junk may be filling the condensate pan after that spray - on cleaner was used .If that evap coil was dirty to begin with ,then an actual washing may have to be done to really clean the coil AND drain line .Those "S" style evap fins make it awful hard to see thru the coil when checking for dirt. Is that a variable speed blower motor? Maybe the e-z trap isnt deep enough to "trap "properly? What kind of trap was there before the e-z trap was installed?0 -
Crack?
Also, I would check to see if there is a hairline crack in the pan itself. If it is draining properly and water is not building up inside the pan itself, It might have cracked. I would check there.0 -
check filter
You might try removing the pleated filter and replace it with a cheap throw away and see what happens.0 -
Thanks for the ideas
But the problem was a low charge and freezing up of the coil. I believe it blocked the drain and that is when it would overflow.
Charged it up last Thursday right before I left work. OK for now. Looks like a leak or multiple leaks in the evap coil. Need to re-check it with more pressure in the system and see if I can pinpoint it. Coil under warranty, so no big deal either way.
Just got to find the time to fix it permanently!
Didn't want to leave everyone hanging, hate it myself when someone doesn't follow up.
Don in MO0 -
leaks
That looks like a blue fin coil model and serial number. Last summer I had to replace about 20 york blue fin coils that were bad from the factory that were in service for 3-5 years. Leaks originated in the center of the coils. York had a terrible string of bad coils from there Albuquerque manufacturer. They switched all there production to there kansas facility. York also paid for labor and materials. Worth looking into.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements