Capture AC heat for DWH
tbone52
Posts: 15
Anyone have an experience or opinion on using a heat exchanger on the AC coolent line to heat DWH. I'm looking at the DOUCETTE product for my 4 ton compressor and hooking it up to a 40 gal preheat DWH tank.
?
?
0
Comments
-
Excellent idea
I have used a homemade hx for domestic water preheat for over 20 years. Most of the time it provides 100% of our domestic hot water heat. The only caveat is that you must have a preheat tank rather than using the existing water heater-it's hard to add heat to already hot water. For best results use a small circulator to pump a loop through the hx and preheat tank, controlled so that it operates when the ac is in operation.0