Grundfos Alpha and zone valves and pump curves
timo888
Member Posts: 137
There is a statement on the Taco HVAC site recommending pumps with relatively flat curve if the system has zone valves:
< In systems using zone valves (or manifold valve actuators) select a circulator with a relatively flat pump curve.This minimizes changes in differential pressure as the zone valves open and close. (See TD01, When Zone Valves Close, for additional information.>
<a href="http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf">http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf</a>
What is the Grundfos Alpha's pump curve? Is it possible to drop a Grundfos Alpha into a system with Taco zone valves?
Will the Alpha "learning" mode in any way get bollixed up by the zone valves' opening and closing? Or is the Alpha actually well suited to this scenario?
Will using a single Alpha to supply two zones of different type (indirect water tank and radiators) present a problem? How does the Alpha recognize which of three possible scenarios is in effect-- DHW zone, radiator zone, both?
< In systems using zone valves (or manifold valve actuators) select a circulator with a relatively flat pump curve.This minimizes changes in differential pressure as the zone valves open and close. (See TD01, When Zone Valves Close, for additional information.>
<a href="http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf">http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf</a>
What is the Grundfos Alpha's pump curve? Is it possible to drop a Grundfos Alpha into a system with Taco zone valves?
Will the Alpha "learning" mode in any way get bollixed up by the zone valves' opening and closing? Or is the Alpha actually well suited to this scenario?
Will using a single Alpha to supply two zones of different type (indirect water tank and radiators) present a problem? How does the Alpha recognize which of three possible scenarios is in effect-- DHW zone, radiator zone, both?
0
Comments
-
depends on the mode
if you're in a constant pressure mode, the curve is absolutely flat... you get 6, 9, or 12 feet of head constant as long as you don't exceed the max flow rating.
I don't use autoadapt.
you could get into trouble if you can't balance flow when all zones are open. but as long as there is balancing and you aren't exceeding the ratings and you have priority or the same water temp requirements for all your loads, you can make one pump do many things.Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements