Will 1 1/2 condenser work with 2 ton coil

Options
I have a 960 square foot cabin with a 2 ton coil installed in propane goodman furnace.  Can buy a two year old 1 1/2 ton goodman condenser very cheap, but would it work?

Comments

  • Techman
    Techman Member Posts: 2,144
    Options
    SURE ,IT WILL!

    But,properly ,is a different story. What is the BTU load calc? What is the SHR?[ eh,Brad !]
  • John Mills_5
    John Mills_5 Member Posts: 951
    Options
    Sure

    Some brands don't even have an odd ton coil, they use the next bigger (or even smaller). Just need to do what the manufacturer approves of and use proper sized metering device. Usually not an issue with TXV but with piston. 
  • Brad White
    Brad White Member Posts: 2,398
    Options
    I would be prepared

    to adjust the airflow downward if humidity removal is key to your success. Running 800 cfm over a 2-ton coil with 1.5 tons refrigeration might not drop your air below the dew-point on some days. Depending on your inlet conditions, you may wind up running 500-600 cfm across the evaporator.



    Naturally, do not drop your air below the coil frost point but you knew that. :)
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad