fresh air requirement per EPA
=1/2 air echange per hr.? SO= 25x40x8 space=8000 cubic feet & 1/2 = 4000?
4000/ 60 min. = 66.6 cfm effective ventilation?
4000/ 60 min. = 66.6 cfm effective ventilation?
0
Comments
-
Your math is correct, but
EPA? I have never used the EPA as a standard of ventilation, not to say that you do not have a specific application such as radon mitigation.
But I do not know, so may I back up a bit and ask a question?
What is the application you are ventilating and is it to a code you are adhering such as the IMC? Or ASHRAE 62? (62.1 or 62.2 depending on commercial vs. residential)? Often the standards I apply are expressed as a certain fairly low cfm per SF value plus a specific CFM per Person value, added together. Very few spaces have a direct ACH rate anymore. So, to be of best help, I just wanted to ask."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
luckily
I SMOKE CIGS IF ONLY TO NOT WORRY ABOUT THIS STUFF....sorry 4 caps & bad joke but heres a link http://www.washingtontimes.com/blog/watercooler/2011/apr/25/study-enviro-light-bulbs-can-cause-cancer/0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements