Geothermal buffer tank to low temp radiant
Renewable BTU
Member Posts: 2
My situation is that I have a great 80 gallon geothermal storage tank with some accessories for future use but it only has one cold inlet and one hot outlet. My thinking is that I would like to create a primary loop from the hot outlet to the cold return and install two sets of closly spaced tees off the primary loop. the first set of tees will go to the radiant panel and the second to the geothermal heatpump. I understand the hp will not be getting the coolest water in the tank but would this warrent changing to a fiur tap buffer tank.
Thanks
Thanks
0
Comments
-
Got other tappings?
Electric element tappings? Drain cock tappings? T&T relief valve tappings?
Whose tank is it.
I have a design for incorporating an inlet and outlet on one tapping using concentric fittings, but the annulus is tight and flow restrictive. Heat pumps usually like LOTS of flow...
METhere was an error rendering this rich post.
0 -
geo storage
Thanks Mark,
HTP tank with hx for possible future use an electric element. we could possibly use the taps for the T&P and Drain for the radiant panel although i think they are 3/4 inch. the inlet and outlet taps are 1 1/2 inch at the top of tank0 -
How many Guppies Per Minute (GPM) are you pushing?
That determines tapping size, along with anticipated delta T.
METhere was an error rendering this rich post.
0 -
IF you
pipe it like it's just a fat piece of pipe on a primary loop, and tee off that loop after the tank, then the geo will see the coldest possible return for the longest possible time... you have to heat the whole tank up before the return water starts heating up. also ensures the longest run times and longest off times... no premature mixing.
the only downside is you MUST run the geo circulator whenever there is a heat demand. Some geo units specify real energy hogs for pumps and in those cases I opt for a 4 port buffer strategy so you can only run the geo pump when the geo is actively heating. with the 2 port strategy it must run to extract heat even when the geo compressor is turned off, so you can extract heat from the buffer tank.
If you've got a reasonable primary loop pump though, I think it makes great sense and I think it's superior to the 4 port strategy in every other way... HOW MUCH better is very debatable, of course. which is why when the known parasitic loss of that geo circulator is high, I change strategies.Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements