Historical Heat Load Calc/ Boiler Sizing methods
InTheLeed
Member Posts: 1
I'm looking for information on some historical methods to both size total systems, and to size the boiler itself to these methods after results are reached for heating demand
0
Comments
-
The most famous one
was the "Mills Rule", named for John Mills, one of the pioneering geniuses of steam and hot-water heating. If memory serves, it went like this:
1. Measure the square footage of glass and divide by 2.
2. Measure the square footage of walls, ceilings and floors that are exposed to the outside and divide by 20.
3. Measure the volume of the room in cubic feet and divide by 200.
4. Add the results of 1, 2 and 3 to get the EDR needed.
There were other rule-of-thumb methods, but I believe all of them were based on Mills' rule.
Once you knew your EDR, you would then size your piping to carry the needed amount of steam or water at a very low pressure drop. On steam this meant a drop of 1 ounce in 100 feet for the smaller systems.
Coal-fired boilers were sized to be able to heat the radiation to its maximum capacity for at least 8 hours on the coldest day of the year, without having to add more coal during that time. This invariably resulted in some seriously oversized boilers, which made things interesting when it came time to convert them to oil or gas!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I'm wondering....
Exactly how accurate was Mr Mills method? Has anyone gone and done a new style loss calc to confirm his numbers?
To the original poster, what exactly is it that you are looking for? Can you be more specific?
METhere was an error rendering this rich post.
0 -
Dan actually did that once
it's in his out-of-print book "Ye Compleate Workes of Dan Holohan" which is a collection of articles he had written up to that time. I'll look it up when I get a chance.
Hey Dan, while I think of it- how about "Compleate Workes, Volume 2"?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Worth thinking about.
Thanks, Steamhead.
Mark, Mr. Mills' Rule will give you about 19% more than you need.Retired and loving it.0 -
Thanks Dan...
Them was some SMART Dead Men.
How did they know?? Like Gil Carlson, I guess they just "Got it".
METhere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements