Roland_18
Roland_18 Member Posts: 147
Hi All,

If I were to use a garden variety "glass lined " water heater as a means to increase the thermal mass of my heating system, would it be necessary to use an expansion tank as well? Also, assuming the water heater is to be used only as a storage tank (electric elements/burner disabled) , how long could I expect the W/H to last? There would be no regular additions of fresh water as it would be a closed system.

TIA, Roland

Comments

  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    Tank volume must be taken into consideration on expansion tank sizing...

    And you COULD put the exp. tank on the additional storage, but you must make sure that there is only one point of no pressure change (connection point of the actual expansion tank).



    Most tanks have a limitation on the tank tapping, which can work against you as it pertains to required flow. You may have to consider piping it in in parallel as opposed to in series..



    The tanks should last as long as all the other steel components in the system, in fact longer due to glass lining and sacrificial anode.



    ME

    There was an error rendering this rich post.

  • Roland_18
    Roland_18 Member Posts: 147
    W/H Buffer Tank

    Thanks Mark.

    How do you mean "pipe it in paralell" ?  Also, would I need to install a T/P valve ?

    Thanks, Roland
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    edited April 2011
    Parallel...

    The return main goes past the tank, and both the hot and cold lines of the tank are connected to the main. It would probably be a good idea to put a venturri tee in either the hot or cold connection to insure circulation between the tank and the main while the pumps are on. Otherwise, you'd need a small circulator to move water betwixt the two.



    No T&P required as long as there is a pressure relief valve on your heat source.



    ME

    There was an error rendering this rich post.

  • aemeeich
    aemeeich Member Posts: 16
    edited April 2011
    Parallel Buffer Tank Connection

    I just did this exact thing at my own house this spring (still a work in progress though).  I used a 40 gal tank from sears. 



    I used the element tappings for the supply/return water piping since they are 1".  I just capped off the 3/4" tappings on the top of the tank.



    It is piped in parallel with its own pump so that I can tweak the flow rate and turn it off if it isn't needed.
  • Roland_18
    Roland_18 Member Posts: 147
    W/H Buffer Tank

    How is the buffer tank circulator controlled?
  • aemeeich
    aemeeich Member Posts: 16
    Buffer Tank Pump

    When I hook it up in the next couple of weeks or so, I'm going to start by running the buffer tank pump whenever a zone is calling, it'll be piggy-backed on the system pump terminal of the boiler.
  • NRT_Rob
    NRT_Rob Member Posts: 1,013
    if you "turn it off"

    you lose 40 gallons of heated water at some point.



    I think you'd be best served by just keeping it inline at all times.
    Rob Brown
    Designer for Rockport Mechanical
    in beautiful Rockport Maine.
  • aemeeich
    aemeeich Member Posts: 16
    Not truly lost in a conditioned space

    In my particular case, since all the equipment is located in a conditioned space, it wouldn't truly be lost.
  • NRT_Rob
    NRT_Rob Member Posts: 1,013
    ok

    then you could say the same thing about the jacket losses of the tank, and then the question is, why take it offline at all?
    Rob Brown
    Designer for Rockport Mechanical
    in beautiful Rockport Maine.