Hydro Coils
James Day_2
Member Posts: 191
What brand of hydro coils do you guys use? Looking to install hydro coil with mod/con boiler setup. What coils give you the best output at 140 entering water. Thanks, James
0
Comments
-
I like FirstCo units myself.
140 deg output just requires oversizing the coil unit. I put an Aquastat on the return line and set it at 110 (most of the time.) Have done this many times with a Vitodens with good success.0 -
First Co.
i use these as well good unit fair price and i have had very few problems with them. i like to strap a 6006C on the return inside the air handler as well works great.
David
aka DrPepper0