Buffer Tanks

servicetech
servicetech Member Posts: 1
Hello - I have an application where two wall mount, low mass condensing boilers are serving a make up air ventilation unit with hydronic coil and a water coil unit heater used for space heating. The load for the makeup air unit is 254 Mbh and the unit heater is 60 Mbh. The primary system is configured with a dedicated boiler pump serving each modulating boiler. The secondary system, also a low mass system, houses the MUA unit and unit heater and is served with a single circulator.

My question focuses on the low mass application. I was planning on decoupling the boiler loop from the secondary loop with a low loss header. The boiler loop hold approx 20 Imp gallons and the secondary systems holds approx. 35 imp. gallons. Is the low loss header enough, or should a buffer tank in the secondary system be considered. Currently, the boilers can modulate to match Btuh demands of the mua unit and the unit heater?

Thanks in advance

servicetech

Comments

  • CMadatMe
    CMadatMe Member Posts: 3,086
    Cascading

    What are the modulation rates of the boilers and will they be cascading? Whose mod/con are you using?

    There was an error rendering this rich post.

  • Brad White
    Brad White Member Posts: 2,399
    You can also

    combine the buffer tank with a hydronic separator, such as a Boiler Buddy. A large tank with large taps to do double-duty.



    I think what you are finding is that make-up air units and unit heaters, being low mass and with rapid transfer (moving air) require a relatively constant flow of water. With low mass boilers, this can lead to short-cycling when demands are sudden/immediate, so having a hydronic piggy-bank makes sense. That is, if I gather your application correctly.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad
  • JohnNY
    JohnNY Member Posts: 3,287
    Hi, Brad.

    I'll tell ya'. I like that Boiler Buddy, but the one-year warranty scares me.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • Brad White
    Brad White Member Posts: 2,399
    Hey John!

    One year warranty?? I did not know that. Too bad. I wonder why that might be, so will ask HTP.



    I think instead of specifying a time-based warranty, I will just ask that the warranty be longer than one of Charlie Sheen's tantrums. :)



    Thanks, John- you got me thinking as usual.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad