Loud Bangs from Weil McLain Boiler - Steam Heat System
Ritzy
Member Posts: 34
In 2001, I had a new Weil McClain (45) Gas boiler replace an
old Weil McClain Gas boiler (75). The plumber told me that the old boiler
was too big for my house (1200 sq. ft.); however, the new gas boiler did not
provide the same kind of even, comfortable heat that the old gas boiler
provided.
Be that as it may, after about 5 yrs. (in about 2005-2006), this new gas boiler
began to began to BANG LOUDLY for 3-5 minutes as it started-up. Although
the steam pipes throughout the house have made banging sounds themselves,
intermittently, we realized that the radiators should be elevated on one side
(with a piece of wood) to reduce this water hammer. We took care of that
problem years ago.
Presently, the LOUD BANGING sounds from the
boiler itself come from the back of the boiler that faces the chimney
wall. These LOUD BANGING sounds give
the impression that the boiler is about to explode....visitors to my house
(and, my family) have been terrified by these sounds. These LOUD
BANGING sounds occur just after the pilot light kicks-on the ignition...just as
the boiler begins to operate. The LOUD
BANGING sounds continue for about 3-5 minutes as the boiler warms up. Two
plumbers have looked at the boiler and could not determine what is causing
these loud banging sounds.
I have taken a bucket of water from the boiler once every 2-3 weeks
throughout each heating season and replaced it from the water feed. The
glass tube is clear and is kept, always, at about 1/2 full level.
Literally, these loud banging sounds, originating from the boiler itself, scare
me tremendously. Anyone have any suggestions to correct this
problem? I have attached a picture of the boiler.
old Weil McClain Gas boiler (75). The plumber told me that the old boiler
was too big for my house (1200 sq. ft.); however, the new gas boiler did not
provide the same kind of even, comfortable heat that the old gas boiler
provided.
Be that as it may, after about 5 yrs. (in about 2005-2006), this new gas boiler
began to began to BANG LOUDLY for 3-5 minutes as it started-up. Although
the steam pipes throughout the house have made banging sounds themselves,
intermittently, we realized that the radiators should be elevated on one side
(with a piece of wood) to reduce this water hammer. We took care of that
problem years ago.
Presently, the LOUD BANGING sounds from the
boiler itself come from the back of the boiler that faces the chimney
wall. These LOUD BANGING sounds give
the impression that the boiler is about to explode....visitors to my house
(and, my family) have been terrified by these sounds. These LOUD
BANGING sounds occur just after the pilot light kicks-on the ignition...just as
the boiler begins to operate. The LOUD
BANGING sounds continue for about 3-5 minutes as the boiler warms up. Two
plumbers have looked at the boiler and could not determine what is causing
these loud banging sounds.
I have taken a bucket of water from the boiler once every 2-3 weeks
throughout each heating season and replaced it from the water feed. The
glass tube is clear and is kept, always, at about 1/2 full level.
Literally, these loud banging sounds, originating from the boiler itself, scare
me tremendously. Anyone have any suggestions to correct this
problem? I have attached a picture of the boiler.
0
Comments
-
Mud?
I don't have a lot of experience with this, but it sounds like there may be a buildup of mud or sediment in the back of the boiler. the only way to know is drain it down and flush it out with a wand.
Others here would know better than me.0 -
I would check to see if
the returns are clogged and how clean the boiler is, inside. What leads me to this is that the problem started relatively recently and degraded to this, rather than on Day-One.
If the return to the boiler is lessened or the boiler has a lot of rust in the bottom, that uneven heating can trigger hammering, with trapped water below the crud and against the boiler wall opposite the flame, hitting the boiling point.
Normally, but not always, the kind of banging I describe happens once the system is warmed up, but in your case it is on start-up yet it is inside the boiler, so I suspect sediment. -Edit: Mud as Paul said.
What is the condition of the water you remove and do you get any solids out? Have you used any cleaning products in the boiler, such as Squick?"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
Thanks so much!
Thank you for the suggestion. I appreciate it. I have tried to keep the boiler clean by emptying a bucket every 2-3 weeks; however, maybe, that was not enough to keep sediment forming in this boiler. I never had this problem with the prior Weil McClain.0 -
Clear Tube Water
I have never used any cleaning products in the boiler at all. The water that comes out, when I take a bucket off of it, generally is 1/2 rusty. It is never clean...although the tube water is crystal clear.0 -
It may not be the boiler
but a collection from your piping coming back to the boiler. It is a "system" after all! So while you are rodding out your boiler, check your returns. Hopefully there is a plug or valve at the end on a tee."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
I think the fittings for the sight glass
are clogged at least at the lower fitting. When I see crystal clear water in a 5 year old steamer I get suspicious. You may be over filling the boiler and not know it. with the boiler cold and shut off you or your plumber need to see if the lower fitting is clogged. I do this by removing the lower valve stem and inserting a small wire or length of solder through the valve body. HAVE A BUCKET HANDY!. if it is clogged you will get a few dribbles when you remove the steam and a whole bunch after you poke the wire through. This is also a good time to clean or replace your pigtail.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Pigtail has been changed
The system has never been fully emptied since installation; however, the pigtail has been changed. Someone mentioned a Hartford loop problem once...then another plumber I had examine the boiler said that the loop was ok.0 -
I agree with Paul.
sounds like you may need to wash out the boiler..hopefully the installer left a way to do it..gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
what do you guys think about
the loop? i know it wouldnt cause any banging at the start of the cycle but with the nipple being a pretty decent size, it might cause some problems during the cycle. why did he downsize the boiler?? did he check the edr of the house to come to his conclusion??
p.s insulate those pipes!!!0 -
Claimed that Prior Boiler Was Oversized
I just want you all to know that I appreciate all of your suggestions and must shout out a grateful, "Thank you!" for all your input. The fellow who mentioned the Hartford loop suggested that maybe my boiler's "loop" was not set at a proper distance and may be involved in my boiler's noise.
Some overhead pipes in the basement...a short distance from the boiler...have silver, vertical vents on them that have never been removed, cleaned, or changed. Might changing those vents help the situation?0 -
Vents
I think what you are describing are main vents. Usually these are located near the ends of the steam mains and their purpose is to remove as much of the bulk air ahead of the steam with each steam cycle.
Without good main vents, that job falls to the smaller, lower-capacity radiator vents and your house will have more hissing than a Joan Rivers concert.
There is not a direct correlation with banging that I can see, regarding vents, maybe an indirect one in that they will not relieve vacuum when steam condenses. (A sudden vacuum creates a different kind of banging, nothing as violent as you describe."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
Truly Violent Banging
Yes, Brad, this is truly violent banging. If I could afford it, I would change the boiler...if that would help the situation. That's how scary the banging is. I could see my replacing the boiler and the banging still happening if there is a problem with the pipes & venting themselves. Does flushing out the system with a chemical hurt the boiler and/or system in any way? My mother mentioned that her boiler was purged once that way...and she didn't have any banging noises from it beforehand like my boiler emits. Her boiler is the same exact model as my Weil McClain Gas boiler (45). Thank you, again!0 -
try some tsp or mex
these will help flush out your system but you will need to install a shut off valve on your return right by the union. change the boiler drain on the return to a full port ball valve and just follow DH instructions on system flushing. if you need them i will be glad to type them up for you.0 -
Need instructions
Thank you, RD. I would appreciate the DH instructions for flushing...if possible.0 -
Flushing
Hi- Here's a link to a some tips on flushing than Dan (DH) put together.
http://www.heatinghelp.com/article/11/Hot-Tech-Tips/145/How-to-Flush-the-Return-Lines-on-an-Old-Steam-System
Sometimes it is easier to just replace the wet return with new pipe. Copper is okay for this as the wet return is a non steam pipe and copper has an advantage in that it is less likely to corrode than black iron.
- Rod0 -
Thank you
Again, thank you for your suggestions.0 -
Boiler noise, check the pipe hanger tension
Installed a peg 40 steam boiler, loud pinging noise from the boiler
started after a week during heat and cool down, roughly every 30 seconds
for minutes, loud enough to heard through the pipes on the second
floor, making it hard to sleep. Followed multiple post here and
elsewhere as to flushing the system which did not alleviate the issue,
I had already adjusted the pipe hangers before installing the boiler, so no added weight was applied to the boiler during the install; the adjustment was made a week prior to the install. Turns out I had to lift the pipe manifolds via the pipe hangers again to remove any downward weight applied by the piping, after the install; I was careful with the pipe fitting, so the install did not cause the issue .
Luckily I leaned on one of the hangers finding it with less tension as
compared to the initial adjustment . Basically I lifted the manifold to
the point of just lifting the boiler a tiny fraction of an inch, then
backed off the adjustment a couple turns Since readjusting the hangers
there has not been one noise from the boiler. Odd part, the initial
tension should not have changed, as there are 5 hangers on multiple
beams supporting the piping over the boiler which does not have massive
weight, maybe 200- 250 lbs..0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements