evaporator heat load

edow
Member Posts: 17
when an evaporator experiences a heat load increase, the suction pressure
remains constant?
decreases?
varies up and down?
increases?
it would increase correct?
remains constant?
decreases?
varies up and down?
increases?
it would increase correct?
0
Comments
-
It Depends
It depends on the metering device the system is operating with. If the system is equipped with an automatic expansion valve, the low side pressure will remain constant. This is because the purpose of the AEV is to maintain constant evaporator pressure regardless of the load on the system. If, however, the system is operating with a capillary tube or a thermostatic expansion valve, the suction pressure will increase.
If the system has a capillary tube, the suction pressure will increase and so will the evaporator superheat. If the system has a thermostatic expansion valve, the suction pressure will increase but the evaporator superheat will remain constant.
Hope this helps.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements