venting for Slant Fin Intrepid/Smith g-8

Hollis
Hollis Member Posts: 105
Am I understanding that with the power gas gun you CAN vent out the side W/O a chimney ?



If so,..do you have much problems going through a stone foundation?  (It didn't seem like the gas company did with installing a larger supply through it but it was of course much smaller than a vent would be.)

Comments

  • Steamhead
    Steamhead Member Posts: 17,387
    edited March 2011
    You'd need

    a power-venter such as a Field or Tjernlund to do it. Also you'd need to exit the building at least a foot higher than the highest snow accumulation recorded in your area, for obvious reasons.



    Power-venters have moving parts and WILL need servicing. That's one nice thing about chimneys- no moving parts.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting