Mod con troubles
TWar
Member Posts: 6
Hi guys,
I ran into a real head scratcher the other day on a new boiler I installed.
The boiler is an NTI TI200 with a primary/secondary setup. About 2 1/2 months after install it started to make loud banging noises with pressure gauge jumping accordingly indicating boiling in the heat exchanger. After much investigation the problem is still not readily apparent. The primary pump is functioning properly and the boiler and piping has been descaled and flushed thoroughly. The boiler was replaced when the manufacturer could not dignose the problem and 2 1/2 months later it has started again with the new boiler. The funny thing is is that the more work that is done to it the worse it gets. There is definetly flow thru the boiler which is why I cannot figure out the cause of the boiling.
This boiler runs perfectly for me on any other systems I have installed.
Thanks for any help you guys can give.
I ran into a real head scratcher the other day on a new boiler I installed.
The boiler is an NTI TI200 with a primary/secondary setup. About 2 1/2 months after install it started to make loud banging noises with pressure gauge jumping accordingly indicating boiling in the heat exchanger. After much investigation the problem is still not readily apparent. The primary pump is functioning properly and the boiler and piping has been descaled and flushed thoroughly. The boiler was replaced when the manufacturer could not dignose the problem and 2 1/2 months later it has started again with the new boiler. The funny thing is is that the more work that is done to it the worse it gets. There is definetly flow thru the boiler which is why I cannot figure out the cause of the boiling.
This boiler runs perfectly for me on any other systems I have installed.
Thanks for any help you guys can give.
0
Comments
-
Got drawings and pictures?
Sounds like an under circulation, negative pressure fluid condition or over fire condition...
METhere was an error rendering this rich post.
0 -
100 Percent Water?
Any glycol in this system? If so what percentage of mix? What's the pressure gauge say when this happens? Boilers high limit is 250 degrees. I'd also be worried about any glue joints in the vent close to the boiler.There was an error rendering this rich post.
0 -
Tankless
I have installed many of these. Had a issue with one of them and it had a tankless on demand domestic water heater on it? Does yours have a tankless? What is the water pressure coming into the house? What size is primary pump? As Mark said pics would help and a drawing too. ThanksThere was an error rendering this rich post.
0 -
boiling
Any chance you have a leak in the system underground and the boiler is taking on fresh water and you now have a limed up heat exchanger? Does this system have a large amount of water in the system and you filled it with real bad water?0 -
de-scaling
I had one that plugged up the pump(s) with pieces of scale that came out of the heat exchanger. Pulled apart the pumps and poked out the chunks, flushed pipes in both directions. Used a concentrated de-scaler pumped thru the heat exchanger (this was a sight to behold!) and followed up with week-long use of factory supplied cleaner, then treatment. Any time one of those type heat exchangers is exposed to boiling or banging, you are likely to have scale on the inside of the tubes.0 -
problem found
Hey guys,
Thanks for all the input. I found the problem today. There was a whole bunch of garbage in the system. I guess the flushing was not able to clear all of it out. I believe the problem was with the pump used to flush it. It was not powerful enough to flush all the crud out of the floor piping (an old 2" steel pipe goes into the floor to the most distant zones). When it was flushed the water came out clear but after prolonged use the circulators slowly brought more out of the system and deposited it into the boiler. I am now in the process of descaling and will be adding a Fernox iron filter to the system to catch all the random garbage coming out slowly.
Lesson learned on replacing an old cast iron boiler with a new mod con. MAKE SURE THE SYSTEM IS EXTEMELY CLEAN. Also the fact that the old system uses poly-b tubing will make regular maintenance a must as oxidation will keep occuring.0 -
Ouch.
A truckload of crud and non-barrier tubing. Otherwise is this connected to old iron piping?
When connecting to old systems I use a Neptune Filter Feeder plus a wye strainer with full port blow-off valve. Some rare earth magnets in the filter bag to harvest stray iron. Makes life a lot easier. I will have to look up the Fernox filter you mentioned.
For the non-barrier tubing, any chance of getting a plate exchanger in there? Otherwise chemical treatment with O2 scavengers.
But glad you found the issue! I am surprised when the first boiler was changed out this was not evident, assuming it was the same problem."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
Mod con troubles
what is the name of the Fernox iron filter that you used. can you please email me with what you paid for that filter. thanks Bob0 -
Hydro Separator
You may also want to get rid of the pri/sec and install a low loss header. Will give you added protection for the boiler. Plus you can blow it down.There was an error rendering this rich post.
0 -
Caleffi products
use a caleffi dirt seperator on the return line to the boiler it should remove the crud from you system and its easy to clean0 -
Spirotherm combo unit
Spirotherm now has a combined hydraulic seperator/air eliminator/dirt seperator that looks like it'd be the ticket for this type of install. Has anyone tried one of these yet? I've been happy with the Spirovent microbublers in the past, so I was thinking of giving one a try.There was an error rendering this rich post.
0 -
crud
We install wye strainers on any old system being replaced with a Mod/Con.
The heat exchangers are just to tight for all the old crud in these systems.
Scott0 -
Y strainer
I install a Y strainer before the pump on every high efficient boiler.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements