pressure fluctuation
maubin
Member Posts: 11
Hi
I have a Monitron Boiler and worked fine until I turned off all loops except one; the pressure goes way down when system/boiler is not running (asking for heat) and when it does the pressure goes back to 20 psi. The pressure gauge was always steady before that. Any ideas?
Thanks!
Marc
I have a Monitron Boiler and worked fine until I turned off all loops except one; the pressure goes way down when system/boiler is not running (asking for heat) and when it does the pressure goes back to 20 psi. The pressure gauge was always steady before that. Any ideas?
Thanks!
Marc
0
Comments
-
Pressure drop
Why did you close all the loops except for the one? Was there problems before?0 -
Pressure fluctuation
No not really I just didn't need the other loops at this time. Before I turned them off the pressure was fine.0 -
Okay
So when there is no heat call what is the pressure with all loops closed except the one?0 -
Pressure drop
It goes to around 10psi0 -
My thought is
The system is seeing more fluctuation due to the smaller volume with only one zone open.
If it does not drop below 10 then there is no leak. Have you checked the X tank to see if the pressure is correct? Should be 12 psi disconnected from the system. If you do not have more than 2 stories.
Seems like an odd way to control zones. Why the manual disconnect of the zones?0 -
Could be head pressure as well....
Is it pumping away from the expansion tank, but into the boiler?
Does the pressure JUMP from 10 to 20 or increase gradually?
Got pictures?
METhere was an error rendering this rich post.
0 -
pressure fluctuation
Hi
Got home tonight and the boiler pressure gauge was reading between 5 and 10psi. Than a little later the system called for heat and the reading @ 150F with a pressure reading of 20psi. (see picture). The pressure doesn't jump it increase more gradually along with the temperature going up. Could it be the X tank? The way the system was put together doesn't not allow me to check the x tank pressure while disconnected. Is there any other way to check the x tank pressure?
Thanks!0 -
wider angle pic
Got a pic of how everything is plumbed to the boiler?0 -
All indications are...
Bad expansion tank.
If it WAS stable before (or relatively so) and is jumping all over the place now, it indicates a loss of diaphragm pressure. It is still not in dire straits, but needs attention.
Make sure and give it isolation and pressure release capabilities. Watts makes a perfect device for doing this.
METhere was an error rendering this rich post.
0 -
pressure fluctuation
I checked the x tank and when cold and there was no pressure in it so I added 12psi to it which brought back the system to 20psi. If it doesn't work I will replace the x tank and add a valve to it to allow isolation. I will take a picture of the system a little later.
Thanks for the help here!0 -
pressure fluctuation
Well after putting 12psi in the x tank and calling for heat the pressure gauge went up to 30psi so I turned everything off. Maybe I need to empty the system of all water and then add pressure the x tank? Or just replace the x tank? Can I use a x tank for potable water that I can buy at the big store?0 -
Yup...
In order to properly check the air side and or charge the air side, the water side MUST be a ZERO psi.
Get ready for a wet mess.
As you are pumping air into the tank, water will be coming out of the tank and this water MUST be let out, or your efforts are for not.
After total recharge, you can expect some increase in pressure when all zones are heated up, unless the expansion tanks is GROSSLY oversized, which I doubt.
If you see any water on the air side, the tank is shot and needs replaced.
Grab your scuba gear.... Obviously, the make up water should be turned off during this procedure.
METhere was an error rendering this rich post.
0 -
pressure fluctuation
I have my wetsuit on ...So I will shut off the remaining zone (isolate the boiler, tank etc) and remove the water from the system then add pressure in the X tank ( which is model Extrol/Amtrol #15) to 12 psi. Refill the system with water until the boiler pressure gauge indicate 20 psi and then open all zones and call for heat. Does it sound like good plan?
I haven't seen any water on the dry side of the x tank so it might still be good?0 -
boiler pressure
You almost have it right. When you refill the system the boiler gauge should read 12 psi also. So 12 psi in the x tank, and 12 psi at the boiler gauge when refilling the system with water.0 -
# 15 tank...
is the SMALLEST tank Amtrol makes.
Let's see, the last time I saw a # 15 tank on a heating systems was... Wait a minute, I've NEVER seen anything smaller than a # 30 on heating systems.
Expect an elevation in pressure when everything is hot. So long as you don't exceed 24 PSI, you should be fine as frog hair...
Ribit.
METhere was an error rendering this rich post.
0 -
pressure fluctuation
After purging the system and resetting the x tank at 12psi operation is normal. I put water in the system until the boiler pressure gauge reached 20psi; should I keep it at 12psi?
The boiler is a Monitron EH-20 135-s perhaps I should change the X tank for a bigger one? I have about 2200 sf surface with 1/2 pex with oxygen barrier.0 -
Bigger IS better...
unless what you have works, then its irrelevant.
Lower the PSI's to 12 and fire all zones and see what the pressure tops out at. If its below 24, then you're good to go.
But keep an eye n it, cause the air pressure went SOME where...
METhere was an error rendering this rich post.
0 -
pressure fluctuation
Thanks to all!
I'll reduce the pressure to 12psi and fire up the whole system and see what's up!
Marc0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements