I have very eatic super heat on a fixed bore system...pressures are 60 suction head will constantly dance.....superheat will be as much as 20 and as low as zero....what gives
0
Comments
-
superheat
What application is this for? Ambient temps?I would lean towards an undercharged system or a restricted liquid line. What is the design freon and what freon is in the system?What are ur pressurers?0 -
Bad airflow?
I am with Techman, a little more information would help tremendously!
But a guess is a guess, check your airflow, bad capacitor on blower motor, bad bearing on small self contained, what ever would make your airflow inconsistant.
Don in MO0 -
Gotta add a third to that guess.
I would start with airflow as well. That is the normal culprit with erratic superheat.
More info would help us narrow it down.0