I don't have a copy of NFPA211- Can I vent an oil boiler and a pellet stove in the same chimney ?

Comments

  • billtwocase
    billtwocase Member Posts: 2,385
    Why vent

    the pellet stove in a chimney? They sidewall vent normally
  • dynamic
    dynamic Member Posts: 20
    Hearth in middle

    My customer has a hearth in the middle of the living room. He is taking out a wood stove for insurance reasons and wants to add a pellet stove.
  • billtwocase
    billtwocase Member Posts: 2,385
    There should have been

    a separate flue, if the wood stove was legal, or installed to code. Are you sue that is a common flue?
  • Eric_32
    Eric_32 Member Posts: 267
    I don't believe..

    there are any pellet stoves that are designed to vent into a chimney. You can drop a liner down the chimney for a pellet stove, but only if it is NOT serving any another applance.

    Read the manual from the stove, or call them and ask for their input.
  • Jack
    Jack Member Posts: 1,048
    pellet stoves are

    not negative pressure appliances. They have a positive pressure vent system. A chimney for your oil appliance is a negative pressure system. You cannot combine the two. As well NFPA 31 specifically prohibits solid fuel and oil venting into the same flue.