oil control
brownie
Member Posts: 1
i have a lennox OF23 oil fired lo boy warm air furnace with a beckett af2 burner bcc3 control center had a honeywell 8184g burner relay right now therm calls burner starts runs then goes off on limit . blower does not start. loose blue low volt wire went to previous 8184m but do not know if wiring correct to either control. only 120 volt on bcc control correct can anybody help, already downloaded manual from lennox .
0
Comments
-
burner control
who changed the controller?0 -
wiring
without pics, one would only guess what has been done. If you have a fan center, "T-T" goes there first. If it is going to the cad cell relay directly, the fan board has no idea there is a call for heat to run the blower. Pics and more info needed, for me anyway0 -
Proper Operation
When limit opens on that furnace, it is supposed to drop 24 volts coming out of board to t-stat and blower should run non stop until limit closes. If it is not doing that, something is wrong. You will need a pro.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements