Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Aquast relay Ll814G
Options
Bigcat
Member Posts: 6
Hi guys.
I have a old american stranded gas furnace that craped out.
I have had a serviceman look at it last season he changed the gas valve,it ran a month and now it's dead again, I called him he said it must be the valve again?.
Being a heavy equipment mechanic for 40 years, i figured I would check it out myself.I can read a volt meter.
This is what I have aquastat relay L1814g
When I test the thermostat lugs TV and T .27 volts I can hear it working when I work the thermostat.
Testing circulator C1 and C2 121 volts
Testing L1 and L2 121 volts
The B1 and B2 are dead .
My Question is what voltage should I have at the B1 and B2?
My next question is I have done a search and can not find the G model is the J a replacement?
Thanks for looking John
I have a old american stranded gas furnace that craped out.
I have had a serviceman look at it last season he changed the gas valve,it ran a month and now it's dead again, I called him he said it must be the valve again?.
Being a heavy equipment mechanic for 40 years, i figured I would check it out myself.I can read a volt meter.
This is what I have aquastat relay L1814g
When I test the thermostat lugs TV and T .27 volts I can hear it working when I work the thermostat.
Testing circulator C1 and C2 121 volts
Testing L1 and L2 121 volts
The B1 and B2 are dead .
My Question is what voltage should I have at the B1 and B2?
My next question is I have done a search and can not find the G model is the J a replacement?
Thanks for looking John
0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 160 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 27 Recall Announcements