Aquast relay Ll814G

Bigcat
Member Posts: 6
Hi guys.
I have a old american stranded gas furnace that craped out.
I have had a serviceman look at it last season he changed the gas valve,it ran a month and now it's dead again, I called him he said it must be the valve again?.
Being a heavy equipment mechanic for 40 years, i figured I would check it out myself.I can read a volt meter.
This is what I have aquastat relay L1814g
When I test the thermostat lugs TV and T .27 volts I can hear it working when I work the thermostat.
Testing circulator C1 and C2 121 volts
Testing L1 and L2 121 volts
The B1 and B2 are dead .
My Question is what voltage should I have at the B1 and B2?
My next question is I have done a search and can not find the G model is the J a replacement?
Thanks for looking John
I have a old american stranded gas furnace that craped out.
I have had a serviceman look at it last season he changed the gas valve,it ran a month and now it's dead again, I called him he said it must be the valve again?.
Being a heavy equipment mechanic for 40 years, i figured I would check it out myself.I can read a volt meter.
This is what I have aquastat relay L1814g
When I test the thermostat lugs TV and T .27 volts I can hear it working when I work the thermostat.
Testing circulator C1 and C2 121 volts
Testing L1 and L2 121 volts
The B1 and B2 are dead .
My Question is what voltage should I have at the B1 and B2?
My next question is I have done a search and can not find the G model is the J a replacement?
Thanks for looking John
0
This discussion has been closed.
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 975 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements