Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

zone valve and boilermate

Options
My electrician has retired. I'm trying to put in a used boilermate thats kicking around the shop probono. Is not there a way to have the boilermate thermostat speak directly to the zone valve?

Comments

  • Alan (California Radiant) Forbes
    Options
    Old Days

    Many a system was wired to directly operate a zone valve through a thermostat.  The thermostat is wired in series with the zone valve so when the thermostat calls for heat, it will complete the circuit of 24 volts to the zone valve.  The zone valve opens and the zone valve end switch closes, turning on the boiler and pump.  No?
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
This discussion has been closed.