Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

zone valve and boilermate

Options
My electrician has retired. I'm trying to put in a used boilermate thats kicking around the shop probono. Is not there a way to have the boilermate thermostat speak directly to the zone valve?

Comments

  • kcopp
    kcopp Member Posts: 4,433
    Options
    wire it as you....

    would any tstat. Taco, Honeywell or which type?
  • billtwocase
    billtwocase Member Posts: 2,385
    Options
    which control?

    Smart control or Z ? As Kcopp said, wire it like any zone, just use the wiring diagram
  • Eric_32
    Eric_32 Member Posts: 267
    Options
    on the smart control

    the two orange wires are the end switch that closes that you would use for a zone valve. Wire those like you would a tstat to a zone valve, or into a multi box for zone valves.

    There is no power on the orange wires they are a dry contact.
  • billtwocase
    billtwocase Member Posts: 2,385
    Options
    personally

    I would get the retro-fit "Z" control for it, and throw the Smart control away. You'll be doing someone a big favor
  • Eric_32
    Eric_32 Member Posts: 267
    edited February 2011
    Options
    UGG..

    nothing worse than getting a call for a buzzing sound from "my blue Amtrol". Every one I've installed at one point or another has came back for issues.

    We've been installing Triangle Tube smart tanks now, nice and basic and no buzzing.
This discussion has been closed.