Axeman vesta boiler
Marilyn_4
Member Posts: 26
Axeman boiler, vesta series. Becket burner
Puff back when I got to the job. replaced nozzle .65 60 A, Filter, strainer, New transformer, draft regulator.
Fire looks bad. Hits the back wall. Target wall looks cracked and red hot.
I can't get the fire to look good.
Can it be the wrong nozzle?
Does the chamber have to be replaced?
Puff back when I got to the job. replaced nozzle .65 60 A, Filter, strainer, New transformer, draft regulator.
Fire looks bad. Hits the back wall. Target wall looks cracked and red hot.
I can't get the fire to look good.
Can it be the wrong nozzle?
Does the chamber have to be replaced?
0
Comments
-
If that's the PVT-105B
with an F-head Beckett, the spec nozzle is a 0.75x80°B at 100 PSI. A 60°nozzle might produce the symptoms you found, even if it's an A rather than a B.
I'd raise the pump pressure to 150 PSI and use a 0.60x80°B nozzle. This will maintain the proper firing rate but burn cleaner. If the boiler is oversized, use this nozzle at 140 PSI for a slightly lower rate, but be sure the stack temp doesn't get too low. Make a label showing the nozzle size and pump pressure you used, and put it on the burner for the next person.
Also be sure the Z dimension is properly set.
And yes, replace the chamber. This is a dry-base steel boiler and a bad chamber can let the flame burn up the base. Then it'll be time for a new boiler.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Vest boiler
Thank you for your reply. I contacted Beckett. They recommended the lowest firing rate to be a .75 and the angle as 80B. Cleaned up the fire nicely. I kept the pump pressure at 100 per Beckett's instructions. 60 degree isn't right for this burner. Maybe that's what caused the puff back to begin with.
I don't know how the boiler was running. The electrodes, when I got them, were pointed down and not even near the nozzle. Not to mention the transformer was not working....well I guess it kicked on once to start the fire and puff back. I'm not sure if the draft regulator blew off or was never there.....
Thanks again,
Marilyn0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements