Mystery

Options
Irv
Irv Member Posts: 95
So I Just had my steam boiler tune up and I observe the

following:

it sounds louder

the water in the guage is more active

some rads which were never a problem now have wet steam sounds

appreciate your thoughts gentlemen

thanks.......

Comments

  • Mike Kusiak_2
    Mike Kusiak_2 Member Posts: 604
    Options
    What did he do?

    Did the tech clean the boiler? Change the nozzle? If the boiler was sooted up, it might not have been operating as efficiently as it is now after cleaning. So now it is generating more steam and behaving as if it was firing at a higher rate.



    Did he make any changes to the burner which might have increased the firing rate? Any changes to the steam side of the system?
  • Irv
    Irv Member Posts: 95
    Options
    mystery

    The boiler was cleaned and replaced with a 1.25 nozzle which is what has been used in the past. I'm wondering that if in fact the boiler is firing at a higher rate if the size of the nozzle could be reduced. Or, maybe the tech without realizing it, put in the wrong size nozzle? Nothing was done to the steam side, I did however recently clean out the pigtail which was a little restricted.



    Thanks.................................
  • Steamhead
    Steamhead Member Posts: 16,842
    Options
    What make and model

    is your boiler? What burner is on it? 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Irv
    Irv Member Posts: 95
    Options
    n

    Its a Peerless JOTTW150S with a Beckett AFG burner
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,322
    Options
    Oil for your boiler

    with that nozzle is to be 140 psi. he may have set it higher or the boiler was just that dirty before. What is the pressuretrol set at? Did it get moved?
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Irv
    Irv Member Posts: 95
    Options
    The pressuretrol

    is set a .5/ with the inside wheel at 1

    The pressuretrol did not get moved.

    What would happen if I reduced the nozzle size?
  • Brad White
    Brad White Member Posts: 2,398
    Options
    Mystery

    Col. Mustard. In the Boiler Room. With a wrench, bucket and TSP...



    I suspect that the cleaning may have been a normal TSP or caustic soda cleaning but was allowed to steam. This in turn can loosen material and oils from the piping that was just happy to sit there. Any additional oils, pipe dope, etc. is just a bonus. Was it skimmed or just cleaned and flushed?



    I suspect at least another good day of skimming is in order, very slowly and sub-boiling. Water bounce and wet steam, go hand in hand, amplified if not caused by dirty water.  Lower pressure actually makes for a more violent waterline, but if clean, the sight glass should hold fairly steady.



    Draw off some water from the boiler surface into a pan and put it on your stove. See how that boils compared to good clean tap water. Any foaming in the boiler sample?



    My money would be on skimming it.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad
  • Irv
    Irv Member Posts: 95
    Options
    For clarification

    The boiler tune up was just cleaning out the combustion chamber

    nozzle etc. No water was touched.

    Thanks