Mystery
Irv
Member Posts: 95
So I Just had my steam boiler tune up and I observe the
following:
it sounds louder
the water in the guage is more active
some rads which were never a problem now have wet steam sounds
appreciate your thoughts gentlemen
thanks.......
following:
it sounds louder
the water in the guage is more active
some rads which were never a problem now have wet steam sounds
appreciate your thoughts gentlemen
thanks.......
0
Comments
-
What did he do?
Did the tech clean the boiler? Change the nozzle? If the boiler was sooted up, it might not have been operating as efficiently as it is now after cleaning. So now it is generating more steam and behaving as if it was firing at a higher rate.
Did he make any changes to the burner which might have increased the firing rate? Any changes to the steam side of the system?0 -
mystery
The boiler was cleaned and replaced with a 1.25 nozzle which is what has been used in the past. I'm wondering that if in fact the boiler is firing at a higher rate if the size of the nozzle could be reduced. Or, maybe the tech without realizing it, put in the wrong size nozzle? Nothing was done to the steam side, I did however recently clean out the pigtail which was a little restricted.
Thanks.................................0 -
What make and model
is your boiler? What burner is on it?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
n
Its a Peerless JOTTW150S with a Beckett AFG burner0 -
Oil for your boiler
with that nozzle is to be 140 psi. he may have set it higher or the boiler was just that dirty before. What is the pressuretrol set at? Did it get moved?Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
The pressuretrol
is set a .5/ with the inside wheel at 1
The pressuretrol did not get moved.
What would happen if I reduced the nozzle size?0 -
Mystery
Col. Mustard. In the Boiler Room. With a wrench, bucket and TSP...
I suspect that the cleaning may have been a normal TSP or caustic soda cleaning but was allowed to steam. This in turn can loosen material and oils from the piping that was just happy to sit there. Any additional oils, pipe dope, etc. is just a bonus. Was it skimmed or just cleaned and flushed?
I suspect at least another good day of skimming is in order, very slowly and sub-boiling. Water bounce and wet steam, go hand in hand, amplified if not caused by dirty water. Lower pressure actually makes for a more violent waterline, but if clean, the sight glass should hold fairly steady.
Draw off some water from the boiler surface into a pan and put it on your stove. See how that boils compared to good clean tap water. Any foaming in the boiler sample?
My money would be on skimming it."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
For clarification
The boiler tune up was just cleaning out the combustion chamber
nozzle etc. No water was touched.
Thanks0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements