baseboard heat 180 degrees not keeping house warm
Bob C._2
Member Posts: 33
looking for thoughts zone valves open- pipes are extremely hot 180 degrees pump running boiler cast iron 18 years old- fins on baseboard dirty-(what is best way to clean)house wont go above 65 past winters did older couple likes to keep 75-80 any thoughts suggestions?
0
Comments
-
Baseboard
Clean the fins on the baseboard (BB) with a vacuum cleaner or brush, make sure the louver is open and confirm that there is at least 2" below the BB to allow cooler air to be pulled in, heated and then vented out the top.
I've seen flooring installed that blocks this space. Without air circulation, there's nothing to heat.
It could also be that not enough BB was installed to heat the room properly.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
not enough heat
is element installed the right way so air can flow through the aluminum fins? was new rug installed? was circulator changed on the boiler and not right size pump installed? Is temp guage on boiler accurate is it really 180* water leaving the boiler? good luck let us know what needed to be fixed to correct the problem.0 -
temps
If this system heated properly last year with the same outdoor temps then You need to check the. return line temperature. If the supply is 180* the return should be 160*.
You could have a restriction to flow. Pump may have a blockage in the impeller.
If the flow is too low then the water looses all of it's heat in the first few feet.
Check your flow...0 -
Pressure/air
Is there enough pressure in the boiler to push the water high enough to fill the system? Is theeree air in the system? Is there a valve partially closed? If it worked before what changed?0 -
Pressure/air
Is there enough pressure in the boiler to push the water high enough to fill the system? Is theeree air in the system? Is there a valve partially closed? If it worked before what changed?0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 98 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 909 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements