Near-boiler piping, counter-flow steam

Options
With four mains.  There were two boilers, one was removed before my involvement.  This is a Weil-McLain EG (30 or 35, still not sure. Waiting for Weil-McLain to call back with info about the burner count-it's natural gas).  The near-boiler piping is wrong: for starters, it is sweated copper.  Secondly, per TLAOSH, the header should feed the mains from the top, they currently do not. 



1) In order to get the header to connect from the top and to get away from the bull-head tee feeding them, I will need to create a header and bring two risers from it to feed each of the two mains.  (Each of these mains in turn feed another main, all counter flow and all properly sloped).  I am not sure how to do that.



2) Does a counter-flow system need an equalizer?  In the pics I found so far, there is not one shown.  Also, I have yet to lay my hands on the install recommendations from Weil-McLain for this boiler. 



Any and all help is greatly appreciated.



Thank you,

Mike

Comments

  • Mike Kusiak_2
    Mike Kusiak_2 Member Posts: 604
    Options
    Weil boiler burner count

    EG30 has 3 burners, EG35 has 4
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    Options
    Then it is an EG 30.

    Is it possible/economical/easy to change the burner and turn the boiler into the EG35?  One of the complaints is when the T-stat is turned up over 60 it just runs and runs.  There are other problems I am addressing too, like zero pipe insulation and bad or MIA main air vents.  Even with the increased burner, the boiler is a tad small for the load

    Total load of radiators: 61,200 Btu's and with a pickup factor of 1.3: 79,560.

    EG30 net IBR = 47 MBH

    EG35 net IBR = 55 MBH

    DOE for both = 62 MBH (how can that be??)



    Thank you,

    Mike
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,322
    Options
    Piping is in the

    installation manual.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    edited January 2011
    Options
    Piping in the manual

    I just found the manual.  But, it only shows one main.  I am still not sure how the near-boiler piping should be for this hookup.  Or is the current configuration OK  Any suggestions are still welcome.



    Thank you,

    Mike
  • Rod
    Rod Posts: 2,067
    Options
    Multi Main Counterflow System

    Hi- Here are some pictures of a nice counterflow system done by Steve Gronski , a Rhode Island steam pro. It uses a header and drips to a wet return /Hartford loop.

    - Rod
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    edited January 2011
    Options
    That is beautiful

    Pipe work.  Thank you, Rod.  I am curious though, with the mains being dripped, could they have been brought back into the horizontal pipe off what looks like the equalizer and thus avoiding the Hartford loop?  I ask this because the system is all counter flow and the Hartford loop is not required otherwise.



    Since the connections to the main are parrallel to the mains and not being brought from the top down, is this the reason they are dripped?  Or is it because this is where the condensate in the mains returns to the boiler? 





    Thank you,

    Mike
  • Rod
    Rod Posts: 2,067
    Options
    Multiple Mains/Hartford Loop on a Counterflow System

    Hi Mike -  While a counterflow system theoretically really doesn't need a Hartford loop, the setup, as in the pictures, has its of benefits while only using a few extra fittings.  It provides a wet leg to collect "mud" and gives the cold make up water more of a chance to mix before hitting the hot boiler. (Also notice that the makeup water inlet (and drain valve) is positioned to flush the mud from the short wet return)  Being on the floor takes the weight of the piping and doesn't put strain on the equalizer piping.  Probably the biggest benefit is that it has a Hartford loop which is about the only item a lot of inspectors seem to recognize on a steam system. To these - No Loop = No Pass!



    The purpose of the drip lines is to collect the returning condensate before it drops vertically into the upcoming steam stream from the boiler. The header's purpose is to dry out the steam stream so it doesn't make much sense spraying water (returning condensate) back into the dry steam.

    The counterflow system is the simplest form of steam system and the majority of ones I've seen are in old houses and have one main. The reason I originally saved these pictures as I thought it had a very good approach to dealing with multiple mains on this type of system and also having a good header to help produce dry steam.

    - Rod
  • Danny Scully
    Danny Scully Member Posts: 1,425
    Options
    End of Mains

    Can you take pictures of the end of the mains?
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    Options
    The pics I have

    Show little.  However, I did put a level on every pipe and all pipes lead back to the boiler.  What are you hoping to see with pics of the ends of the mains?



    Thank you,

    Mike
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    Options
    Your description

    Is much appreciated, along with the pics, Rod.  After reading your explanation and then looking more closely at the pics, I see what you mean and it makes sense. 



    Thank you,

    Mike 
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    Options
    Your description

    Is much appreciated, along with the pics, Rod.  After reading your explanation and then looking more closely at the pics, I see what you mean and it makes sense. 



    Thank you,

    Mike 
  • Danny Scully
    Danny Scully Member Posts: 1,425
    Options
    Better Idea

    I just want to get a better idea of the piping, somthing doesn't seem right. Well, a lot doesn't seem right haha.
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    Options
    You are not kidding!

    Aside from the fact it is copper and is sweated together, to me, it seams all wrong, too!  However, I am not sure if at this time, I will tackle the near-boiler piping problems.  I will likely wait until spring - the house is currently warm. : ) 



    Is there any other questions I can answer in the mean time?



    Thank you,

    Mike
  • Danny Scully
    Danny Scully Member Posts: 1,425
    edited February 2011
    Options
    1-1/4

    Where is that 1-1/4 (or 1") line coming from? And where is the fourth main?
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    Options
    The 1 1/4" pipe, is

     Actually a 1" pipe.  This is a completely useless pipe too - it is hooked to the end of a main at the far right side and is higher than the main.  It never gets warm, let alone hot and after placing a level against the main it is connected to, I have determined it does not get warm or hot because the condensate never gets to it.  I am removing it, eventually. 



      I was wrong about four mains - what I thought was the fourth main is actually a branch off of a main on the right side of the boiler.  That pipe is black and you can see the take off from a silver main on the third picture, I think it is.  It heads up and left.



    Thank you,

    Mike