Uphill Return
Magiccontrols
Member Posts: 1
I have been asked to do a job in a factory where they want to have some steam fin tube radiation installed at the bottom of an elevator shaft. The condensate return line is about 20 feet above the bottom of the elevator shaft. I was told that there used to be a radiator there and the steam was piped into the radiator and the condensate was piped back up to the condensate line without a pump. The piping is still there but the radiator has been removed and the lines are capped at the bottom of the elevator shaft. There is still a bucket steam trap up at the condensate return line right before it ties into the main condensate return. Is it possible that this could have worked? There is 20 pounds of steam pressure.
Thanks
Thanks
0
Comments
-
YES
20 pounds of pressure is enough to lift a column of water about 50 feet. So, if the steam pressure is 20 psi, and the steam is always up, it will work just fine. However, anytime that the steam pressure is down and then comes back up, you are likely to get a little bit of hammering before it pushes the condensate out.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
bucket traps
in TLAOSH Dan talks about how bucket traps are used to lift condensate .. and I don't think it required significant pressures. in fact pressures of that range may harm bucket traps .. but I'm not exactly certain of the operating limits of the traps.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
found this ..
maybe helpful .. http://www.heatinghelp.com/article/163/Older-Steam-Heating-Systems/1314/Inverted-Bucket-Traps1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements