steam question
jimbo123
Member Posts: 3
If the setting of a pressuretrol for a boiler is lower then the required pressure needed to overcome the frictional loss in a pipe will that boiler ever make pressure.
0
Comments
-
operating pressure loss
in a small system, the operating pressure can still be very low, without causing the system to be inoperative. elsewhere here is described a medium sized system which operates on 1 ounce!
http://www.heatinghelp.com/forum-thread/134730/Saved-SARCO-Vapor-System
--nbc0 -
Yes and No
It depends where you measure the pressure. If the pressuretrol is set for 1 PSI, and the boiler has the heating capacity that meets or exceeds the heating capacity of the system, it will build pressure up to one PSI at the boiler, at which time the boiler will shut off until the pressure falls. However, if you were to measure the pressure at the end of the line, and if the facts of pressure loss are as you say, then the pressure reading at the end of the line would be 0, at the same time it was 1 psi at the boiler.
That being said, in such a system, you may find that the steam flows everywhere it is supposed to go and the system works just fine.
On my own system, the vaporstat is set to cutout at 8 oz. However, the pressure seldom increases above 2 oz at the boiler. Steam distribution is achieved at 2 oz at the boiler. That is simply the back pressure that is read at the boiler as the boiler is producing steam and pushing it down the steam mains.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements