Are my edr calculation correct...PLEASE help

AJ1
AJ1 Member Posts: 24
I am in the process of sizing a gas fired steam boiler...are my calculation for total EDR correct...

Please help..

also do I need to multiply the total by 1.33 to get the final edr..is this factor of 1.33 needed..

I am also attaching photos of the radiators in case my calculations are off...I was taken into account 2 column and 4 tubes..in my calculation..

my calculations are here..



<a href="https://spreadsheets.google.com/ccc?key=0AoRHjdMocm80dHBTWmJIWXJTMlpBaEFmQXI1UUQyOXc&hl=en&authkey=CMKSstAJ">https://spreadsheets.google.com/ccc?key=0AoRHjdMocm80dHBTWmJIWXJTMlpBaEFmQXI1UUQyOXc&hl=en&authkey=CMKSstAJ</a>



I came to the total of 269 Sq FT EDR without the 1.33 facto and therefore looking at the boiler spec sheet it is giving me a IBR Net Rating Steam (BTU/hr) 64000.



Also in the trade when they say you need a 85000BTU/hr boiler do they mean DOE heating capacity or IBR.

Comments

  • Dave in QCA
    Dave in QCA Member Posts: 1,788
    EDR and BTU

    The EDR rating of a boiler already has the piping and pickup facter figured in.  You simpley match a boiler to your EDR.  If you are using your BTU figures, you would either match your system BTU to the NET BTU rating on the boiler, or take your system BTU x 1.34 and that should match up to the Output (gross) of the boiler.



    I hope that makes sense.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • Steamhead
    Steamhead Member Posts: 17,397
    That column radiator

    looks like an H.B. Smith "Princess" which has a higher EDR per section than the usual type. So if they're all like that, the living room would be 3 SF per section, or 33 SF. The drawing room would be 2.6 SF or so, for 28.6 SF (23" Princess rads don't appear in my charts) or 57.2 for the pair. The foyer would be 4 SF/section for 24 SF, or 48 for the pair. If you can find a name on those column rads, that will help.



    The wall rad, if each section is 22x13 inches, is 7 SF per section, or 56 SF.



    The tube rad shown is a small-tube rather than large-tube, 1.8 SF per section. The 6-section of this type is 10.8 SF, the 10-section 18 SF, or 36 SF for the pair.



    So your total would be 241 SF. You don't need to add a pickup factor when looking at boilers, since that's already figured into the Steam Square Feet rating. A Burnham MegaSteam 288 for oil or Smith G8-S-3 for gas would serve this system very well.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Dave in QCA
    Dave in QCA Member Posts: 1,788
    looked like small tube to me too, but....

    If they the tube style radiators measure 1.75 inches for the width (thickness) of each section, they are small tube radiators.  However, my table differes from Steamheads.  For a 4 tube x 25" tall smalltube radiator, I show 2 sq ft/section.  My table shows 1.6 for a 3 tube, perhaps Steamhead looked at the wrong line on his chart?

    I am attaching my file from an old ASHRAE guide book.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • AJ1
    AJ1 Member Posts: 24
    thank you

    all for your help...

    One last question...I am looking at the boiler spec sheet and in one column it says Input (Btu/hr) and for 270 SQ FT IBR Steam this value is  103 (BTU/hr).



    Refer to Model number BSI103 in the attachment.



    Does this means that I will consume 103 GAS THERMS if I operate this boiler for one hour.



    Reason for asking is,that I am trying to find out what my gas bills would be like..if I go with this boiler..
  • Mike Kusiak_2
    Mike Kusiak_2 Member Posts: 604
    Therms vs. BTU

    If the boiler spec for input is 103, 000 BTU/hr, them this corresponds almost exactly to a fuel useage of 1 therm per hour. Of course this only applies while the boiler is being fired, and under normal conditions it will not fire continuously. The boiler will cycle on and off under the control of the thermostat and pressuretrol to meet the actual heat requirements of the building.