half of the pipes in basement not getting steam
mikest315
Member Posts: 1
Thank you everybody who participates in this forum. I just bought an old house and I have learned a lot from all of you. When I first bought my house a month ago, all the radiators worked. However, the radiators in the back of the house no longer work. I went in the basement, and discovered one of the pipes leading to those radiators is cold. This pipe has a vent on the top. I tried taking a picture but it may be tough to see. Should replacing this vent solve the problem?
Thanks, Mike
Thanks, Mike
0
Comments
-
lazy steam
you can turn the system off, and when cool, remove the vent, and re-fire. when steam comes out the vent opening, you know that the pipe has no obstructions in it, such as a sag, or water puddle, preventing the air from escaping so the steam can move. in this case, you need a new vent. be ready to turn the boiler off as soon as you see steam.
if you see no steam, then check the pitch of the pipe with a level. in a complicated pipe run, it helps to put masking tape on the pipe, withe arrows marking the direction of downward slope. on my system, i had an area where the arrows were pointing towards each other! it helped that these areas of dry return had not yet been insulated, but if yours are, then maybe a nail at each end of the level will pierce the insulation enough to give you a reading.--nbc0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements