Uponor/Wirsbo A3030004 controler fuse keeps blowing
bob_48
Member Posts: 4
The fuse blew on my Uponor/Wirsbo A3030004 radiant controller for the first time.. It had a 2 amp fuse in it. The system is about 4-5 years old.
I replaced the fuse and turned the power back on, after about 15 seconds I heard the zone pump/valve go on, and saw the fuse flash and burn out again.
Just to test it, I replaced the fuse again, this time with a 3 amp fuse (as the controller said dont go higher than a 4 amp fuse). This time the 3 amp didnt burn out.
I am trying to determine if there is something else wrong that would make this kind of behavior happen. Would the controler board be bad? valve/pump? ???
I have the 3 amp in there now so I can get heat...but I want to make sure I am not going to cause other problems.
Thanks,
bob
I replaced the fuse and turned the power back on, after about 15 seconds I heard the zone pump/valve go on, and saw the fuse flash and burn out again.
Just to test it, I replaced the fuse again, this time with a 3 amp fuse (as the controller said dont go higher than a 4 amp fuse). This time the 3 amp didnt burn out.
I am trying to determine if there is something else wrong that would make this kind of behavior happen. Would the controler board be bad? valve/pump? ???
I have the 3 amp in there now so I can get heat...but I want to make sure I am not going to cause other problems.
Thanks,
bob
0
Comments
-
fuse blows
Something is obviously drawing overcurrent on the fuse. You may have a wiring issue or the zone valve is going bad and pulling too much amperage. A good test meter will help you diagnose the problem.0 -
ZCM's
there was a recall on certain zone control modules from Uponor 4-5 years ago. you'd have to check their tech documents to determine if yours is one of the problem units. Their relatively inexpensive, so replacement is the way to go.0 -
Possible problem found
I didnt notice it before but after looking more closely at the manifold I saw that one had a slight drip under on of the valves. I pulled off the accuator and saw moisture underneat it and some sticky deposits on the valve...possible from the fluid inside (not being just water).
So I believe I probably have a bad valve and/or its accuator or both. I am going to put a meter on it to verify. I am also going to put back a 2 amp fuse and take the accuator off the valve that appears to be wet and see if the fuse blows.
Thanks,
bob0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements