economizer???

Paul S_3
Paul S_3 Member Posts: 1,277
hey everyone. im having trouble with a york packaged unit with a w7212 honeywell economizer. i have been to this job twice for no heat. upon arrival i found the heat running normal, but also find the economizer in the fully open position. i disconnect the plug and reconnect it and it closes, then come back to find it open. if im not mistaken i thought the economizer only opens on a call for a/c, depending on the enthalpy control am i missing something???
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Al Letellier_21
    Al Letellier_21 Member Posts: 402
    economizer

    Sounds like an issue with either the motor or the enthalpy controller....does your unit use the economizer for exhaust, ventilation or outside air control.....this can happen in either heating or cooling...sounds like some more trouble shooting is in order. Is the unit on an energy management system and are the settings correct?
  • Paul S_3
    Paul S_3 Member Posts: 1,277
    economizer

    all its for is free cooling during the a/c mode. its a 7.5 ton york packaged unit
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Paul S_3
    Paul S_3 Member Posts: 1,277
    economizer

    all its for is free cooling during the a/c mode. its a 7.5 ton york packaged unit
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Al Letellier_21
    Al Letellier_21 Member Posts: 402
    economizer

    Still sounds like an issue with the control or the motor. Try the AC section of the Wall for more help.