Sealing Steam Pipe Chases
richelle
Member Posts: 2
I have a question about sealing the gap between the floors/ceilings and the steam risers. We had an energy audit that found that we have more than one air change per hour. Among the recommendations were to seal off the unconditioned portions of the building from the conditions portions including sealing any gaps between the steam risers (one pipe steam) and the floors or ceilings. They recommended a firestop foam sealant, such as DAP® FIREBLOCK FOAM Polyurethane Foam Sealant, which states that it has a safe temperature range of -200°F – 240°F.
Before spraying it the gap and not being able to get it back out, I wanted to check and see if this was safe. Given that water boils at 212°F, it seems like the radiator pipe could get warm enough to exceed the maximum recommended temperature.
If this isn't a good idea, does anyone have any other air sealing recommendations that can come in contact with the risers (or in a few cases the mains)?
Thanks!
Before spraying it the gap and not being able to get it back out, I wanted to check and see if this was safe. Given that water boils at 212°F, it seems like the radiator pipe could get warm enough to exceed the maximum recommended temperature.
If this isn't a good idea, does anyone have any other air sealing recommendations that can come in contact with the risers (or in a few cases the mains)?
Thanks!
0
Comments
-
my header ....
maxes out @ 218 deg F...you should be ok...you can always try it first somewhere in the basement very accessible so you can scrape it off later..
fyi..I have some regular "great stuff red" around a rad supply...and it is holding up fine.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
We've used a similar product
with no problems so far. Not sure if it's DAP's foam though.......All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Yup, that's it
I think it's rated for 400° F or so.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements