Steam stumper...
kcopp
Member Posts: 4,462
Looked at a 3 unit apt today... 1 each floor. 1 steam boiler. T-stat in the bottom unit. strange oddity is that the 1st floor apt does not get heat ... all 4 rads cold but the risers to the 2nd and 3rd are piping hot. I replaced the main vents a while back and can hear them panting. I have a varivalve in the back bathroom rad and still no change.... strange thing is that the riser to the 2nd and 3rd floor and just inches away from the 1st floor rads.. all piping is insulated. ty,kpc
0
Comments
-
questions
1 pipe or 2 pipe? What is the rated capacity and firing rate of the boiler? What is the EDR of the connected radiation. What type of main vents. What type of radiator vents? How is the piping arranged?
It's really hard to comment on your system without knowing the above items.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
lets see...
1 pipe , paralell pipe. Near boiler piping is ok. 1 bull head tee but not real bad. 2 Gorton #1 on each main. the old ones were plugged. Rad vents are various. some gorton D upstairs. the problem floor has 1 varivalve, 1 ventrite. edr is around 500 ft2.0 -
Panting....
Not generating enough steam pressure.
Boiler underfired or leaking steam out of a section into the combustion chamber?
METhere was an error rendering this rich post.
0 -
panting radiators
either they are saying "peel me a grape", or the panting in those rads could be indicating uninsulated piping.
there could also be a problem with the relationship of venting capacity between the radiator vents, and the main vents. if your main vents are not up to the job, then all the air flow will try to escape [aided by the gas company at great expense] by way of the radiator vents. any water being carried along can end up in the vent, and close it with the internal float. so no venting there = no steam coming up!.
try to fire the boiler, with an assistant whose hand is on the switch for quick turning off. take off the vent, while it is off, and then switch it on. i bet you will see steam in those rads. make sure not to allow the steam to flow out the vent tapping for more than a few seconds as it can remove all the wallpaper in minutes!--nbc0 -
The Gorton D's are winning the battle
try c's or smaller up stairs and CHECK for a leak in the boiler. Steam is lazy, remember that!.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
And like Herding Cats!
Yes, steam is lazy, and has a mind of its own! It goes where it wants to, not necessarily where you want it to. Kinda like trying to herd cats. They don't care what you want. They're lazy and they go where they want!Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
thanks...
I will keep at it. The big rad in the living room is a bit better w/ the varivalve.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements