No Main Vents?
jamesylove
Member Posts: 6
I have a 1 pipe steam system and have had some issues getting it balanced. I wanted to check the main vents. However, I've been unable to find any main vents in my basement. The basement is finished, but I can see all of main pipes, except the last section of main that that feeds that last radiator to my 2nd floor. I can access this section of pipe by removing a section of drywall. Is it worth the effort to do this and discover a potential main vent (I'm not very hopeful that one exists)? If there is no vent, should I try to add a vent at this location or another location on the main? I've learned a great deal on this site and appreciate any advice.
0
Comments
-
where is the vent?
use a level to determine the slope of your main. if it is sloping up away from the boiler, then it is a counter-flow, and the vent should be on the end. if it is sloping down from the header, and back around towards the dry return, the it is a parallel flow, and the vent should be at the end of the dry return.
every system needs some way for the air to get out of the main pipes, and since the radiator vents are not up to the job, without a lot of expensive help from the fuel company, main vents are needed. so it is well worth the digging in to the ceiling.--nbc0 -
Old main vent?
I removed a section of drywall near the end of the main. The section
pictured below is about 2' from the last riser that feeds the furthest
radiator on the 2nd floor and about 18" from the end of the main before
it turns down as the return. Do you think this fitting used to be a
vent? Currently, it is just a plug on the fitting. Should I try to remove the plug
and install a vent since I've been unable to find a vent anywhere else
on the main.0 -
angled take-off
normally, a T which is angled on the main like that usually was meant for a radiator takeoff somewhere that was perhaps never installed or removed .. this may be a good place for a vent .. but there probably was not a vent there originally, more likely a radiator. you will probably have a really hard time taking that plug out.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Thanks...
Thanks for your reply, I'm going to try and remove the plug on the T. However, as you can tell from the picture, I do not have a lot of room to work so I may not have enough leverage. But, if I can remove the plug, does the vent need to be perpendicular to the main? i.e. do I need to use another fitting to correctly position the vent on the main0 -
Vent installation
You vent needs to be installed vertically, otherwise the float mechanism in the vent will not be able to work correctly.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Stuck plug
I've soaked the plug with penetrating oil and have used my 18" pipe wrench but I can't break it loose. I don't have room for a larger wrench or a bar on the wrench. I may heat up the Tee and try to loosen it in the next couple of days.
Plan B: since I do not have a main vent I think I may try to tap into the main next to the Tee and add a vent. What are the chances that I somehow damage this section of main by tapping this old pipe? Should I call a pro to add a vent?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements