Advice on vaporstat?
davidsorkin
Member Posts: 18
Hi,
This morning my steam boiler was not firing despite a call for heat. The radiators were slightly warm. After some head scratching I tapped on the pressuretrol with my finger and it started right up. The control is very old and is probably the same age as the boiler from 1979. I would like to replace it with a vaporstat and also get a 0-3 PSI gauge.
I've read on the forum to use a 0-16oz vaporstat - is there any downside to a 0-4 lbs control instead? Since I have never run the system at 16oz I do not know if it would be sufficient. I am looking at the Honeywell models L408J1009 & L408J1017. Does anyone have experiences with these to share?
Also I've been searching the Internet for a 0-3 PSI gauge but have not found many options. I did find Low Pressure Gauges made by Wika and alternatively Ashcroft but I am not sure if they are ideal for steam applications. Does anyone know about these or have another favorite that I might be able to find on the Internet?
Thanks!
David Sorkin, North Plainfield NJ
This morning my steam boiler was not firing despite a call for heat. The radiators were slightly warm. After some head scratching I tapped on the pressuretrol with my finger and it started right up. The control is very old and is probably the same age as the boiler from 1979. I would like to replace it with a vaporstat and also get a 0-3 PSI gauge.
I've read on the forum to use a 0-16oz vaporstat - is there any downside to a 0-4 lbs control instead? Since I have never run the system at 16oz I do not know if it would be sufficient. I am looking at the Honeywell models L408J1009 & L408J1017. Does anyone have experiences with these to share?
Also I've been searching the Internet for a 0-3 PSI gauge but have not found many options. I did find Low Pressure Gauges made by Wika and alternatively Ashcroft but I am not sure if they are ideal for steam applications. Does anyone know about these or have another favorite that I might be able to find on the Internet?
Thanks!
David Sorkin, North Plainfield NJ
0
Comments
-
Vaporstat
Hi David:
You might want to search the Steam forum for answers to your questions. I think I've seen them discussed there before.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Vaporstat?
Thanks Alan - actually I did a lot of reading but haven't found the answers to my specific questions. I did read one additional post though that makes me question using a Honeywell vaporstat at all.
http://www.heatinghelp.com/forum-thread/128249/why-do-Honeywell-vaporstats-suck-so-badly.
What better alternatives are there?
Also - why would a pressure control be used in conjunction with a vaporstat? There's a photo of this setup here:
http://www.heatinghelp.com/forum-thread/129949/Temperature-based-cut-in-for-a-Vaporstat
For the low pressure gauge I found this one http://www.coleparmer.com/catalog/product_view.asp?sku=6893010 but seems a little pricey at $46
Thanks0 -
Clean the pig tail
drop it to 0.5 cut in and 1 differential.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Low Pressure Gauge
I finally got all my plumbing parts and installed the 0-3 PSI Wika low pressure gauge the other night. It took pexsupply a long time to send me all the little brass nipples. The gauge is fantastic and has vindicated the pressure control. I was able to very precisely set the control to cut in at .5 and cut out at 2 lbs. It's strange that the original gauge is 0-30 PSI, it be would like my car having a speedometer that went up to 1,200 miles per hour!0 -
David you need to keep the old gauge
Insurance requires a gauge that is rated twice the relief valve rating of the boiler.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements