I have a commercial building, late 1800s, 40+ rads and 400k btus single pipe steam. I have gained tremendous knowledge on this site and have made huge improvements in getting heat to alot of cold/dead rads. I have a 0-20 oz guage and 0-3 psi guage. I just installed 2 gorton #2's on each main end (4 total) and reduced my readings of (avg.) 10-12 ozs and .5 to 1.0 psi of steam to 1-2 oz and 0-.5psi now. I hope to see much diff in the heating, I'm on day 1 on the main vents, and had single gorton Ds on each B4(2 total). while changing the vents/piping I drained out the water pretty low and did a light skimming. I cleaned the site glass spotless (9am) and by 5pm the water was brown again and site glass almost unreadable. Is there any way to get this water cleaner? I know theres a 100yrs of rust in there, but I see alot of your guys pics and the water is clean. I read about SQUICK and TSP is either better or dont bother? I also have had wet steam from the day I bought this property, its alot better now since reading here, if I pull a vent off a rad and shake its got quite a bit of water in it. I have alot of bounce in my site glass water, it is dirt or needs skimming again? I'll post pics of my setup 2moro, my piping isnto too bad near boiler, it could be better though and im thinkin of repiping the headers in spring after seeing some works of art posted here, makes me kinda jealous......thanks alot guys
0
Comments
-
My boiler was very dirty
too. I flushed it and skimmed it for hours and hours. It got dirty again within minutes. I was unable to get mine clean using normal blowdown methods. When we re-piped we put in the "King valves" that Dan recomended in the following video http://www.heatinghelp.com/article/107/Steam-Heating/118/Steam-boiler-near-boiler-piping Using the Kings to do a pressurised backflush got it clean after about 3 or 4 attempts and it has remained that way ever since. So if you are planning to re-pipe in the spring spend the extra few dollars on the King valves in the video, and yours will be crystal clean too. You don't need chemicals to get it clean, just some valves in the right places.0 -
cleanning the boiler
you could try the method recommended by peerless boilers, which we used on startup: use arm&hammer washing soda. the instructions follow here:
G. CLEAN THE BOILER
1. Clean the boiler as described below no later than
one week after the initial start-up. Cleaning will be
more effective if the boiler operates a day or two to
loosen sediment and impurities in the system.
2. The boiler must be cleaned to remove any
accumulation of oil, grease, sludge, etc. that may be
in the system. These substances can cause foaming
and surging of the boiler water, producing an
unstable water line and water carryover to the system.
3. The piping for a skim valve must be done as shown
in Section 5, “Pipe the Boiler,” of this manual, with
the skim valve mounted off of one of the end riser
connections.
4. Connect a 2 inch drain line off of the skim valve, run
to a point of safe discharge.
5. Close all valves to the system. Provide a means of
continuous fresh water to the boiler for the cleaning
process.
6. Use common washing soda (such as Arm and
Hammer Super Washing Soda). Mix the soda with
water in a 10 quart (9.5 liter) pail and pour into the
boiler through the safety valve tapping. Use a
proportion of one (1) pound (.5 kg) of washing soda
for each 800 square feet (74 m²) EDR net boiler rating.
7. Open the skim valve. Fill the boiler until water begins
to flow out the valve.
8. Turn burners on and allow the boiler water to heat
up to just below steaming [180 to 200ºF (82 to
93ºC)]. Cycle the burners to maintain temperature
during skimming. Do not allow the boiler to steam.
Steaming mixes up the contaminants in the water
instead of floating them at the surface.
9. Open the make-up water valve to continuously feed
water to the boiler. Allow water to flow out of the
skim tapping.
10. Continue skimming the boiler until the water flowing
from the skim tapping flows clear. This will take
some time, possibly several hours for a dirty system.
11. After skimming is complete, close the skim valve and
turn off the boiler.
12. Close the make-up water valve and open the boiler
blowdown valves.
13. Drain the boiler completely. Then refill and drain
again one or two times to make sure all of the soda
has been washed out.
14. Restore piping to normal. Pipe a nipple and cap in
the skim valve.
15. Note: If the gauge glass becomes dirty again, this
indicates more contaminants have worked loose in
the system. Repeat the cleaning and skimming
process as needed to clean the system.
Cleaning the boiler requires the use of very hot water
and corrosive chemicals. Use care when handling to
prevent injury.
WARNING
Do not leave the boiler unattended while firing.
Take great care not to allow the water level to drop
below the bottom of the gauge glass or to allow fresh
water make-up to flow in too fast. This will avoid the
possibility of causing the boiler sections to fractture.0 -
Dirty Water
Hi- You just have to have patience and do repetitious cleanings. You can't expect to make up for 100 years of neglect in just a light flushing or two.
For just cleaning the boiler - You can use TSP or washing soda though that's just to clean the boiler. You can't leave them in the boiler and make steam.
You might try using Rhomar 9150 as one of its advantages is that you can leave it on the boiler for a week or until things get really dirty and then flush it out and repeat the process till your boiler and piping are clean. I've used it and been quite happy with it. I did a couple of boiler plain water flushings first before I used the Rhomar as I saw no sense is wasting it if I could get the primary dirt out with plain water.
http://www.rhomarwater.com/products/residential-steam-system/
Generally I would be cautious about boiler additives. Most of the steam pros seem stay away from them. Other people have used different additives from the ones I 've mentioned but I can't help you on those as the only ones I've using is washing soda and the 9150
Skimming - I've had to skim up to seven times on consecutive Saturdays before my water line finally got settled down. I'd skim for two hours at a time and collect about a 5 gal bucket. It's one of the things that also needs patience. Once you get setup to flush or skim it's fairly easy to do multiple times. If you are loosening and removing a lot of "crud" from you boiler you may want to check your pigtail and connected items afterward just to see none of the loose dirt etc. has clogged them up.
- Rod0 -
thanks
thanks for the responses. I saw the video a while back about the king valves and return valves process, which id love to do. The big problem is the ancient piping has these valves in place, the problem is they look like they belong on a battleship, theyre butt flanged gate valves the size of a basketball, I wouldnt even wanna chance playing with them. Can someone give me some insight or point me in the right direction as fas as cleaning/skimming during heating season. I did it after a cool off of 2 hours on a milder day, but were in dead of winter in NNJ and I am curious if theres a way to do so while still making steam........thanks again for all the great advice0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements