Mister forgetful
Options
wess
Member Posts: 1
I took a one system boiler turned it into a two system. I have two Taco 007 circulators and two Taco flow controls on the system. my problem is that it is a Weil Mclain boiler with a Honeywell L8148E aqustat 1 put a R845A for the second thermostat witch is a T87 but i can not get the boiler to turn on the circulator runs but only when the down stairs thermostat is on will the boiler turn on . I can not remeber how to hook the up stairs thermostat up to make the boiler turn on when either thermostat calls for heat It is a natural gas boiler Any help would be Greatly appreciated Thank you Mister Forgetful
0
Comments
-
There are
two sets of normally open contacts on the R845A; 3 and 4 is one set, 5 and 6 is the other set. You are probably using terminals 3 and 4 power the pump, no? Terminals 5 and 6 can be used to tell the boiler to come on. Wire them to T and TV on your L8148E, but make sure you don't jumper them to line voltage. They should be used as dry contacts, i.e. no power.
http://customer.honeywell.com/techlit/pdf/95-0000s/95-6127.pdf8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements