gorton #2's backordered @ pex

jpf321
jpf321 Member Posts: 1,568
i just heard through a source close to the supply chain .. that there are no Gorton #2's anywhere in the NYC area (which includes pexsupply/gil meyerowitz, simplyplumbing/blackman, amaf,  etc.).. but they seem to be in UPS transit from Gorton to Pexsupply et. al. This information comes a bit late, as they were heavily backordered the last several weeks (I know of someone that ordered them from Pex prior to X-mas who hadn't rec'd them as of last week). I'm waiting on a large (double digit) order of #2s .. when they arrive, I will update this thread. 
1-pipe Homeowner - Queens, NYC

NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics

Comments

  • my order shipped in today

    I Ordered 2 Gordon # 2 s 12/28/10 came in today from pex supply
  • jpf321
    jpf321 Member Posts: 1,568
    thx

    tux for the tidbit...
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • Steve_175
    Steve_175 Member Posts: 238
    It's all your fault

    That's write I am blaming the lot of you on this forum. I contacted Gorton to find out what the hold up was. They said that because of this site there has been a huge surge in demand for the #2's. I. They told me they had a back log of orders they are trying to push thru but the #2's take longer to make. I suggested they should stock up in the summer. They said they had done that and had 600 ready and then poof they were gone. I ordered 6 on 12/26. Was told today I will get them in 3-5 BD.

    BTW everyone needs to contact them and tell them to develop a #3. If they get enough request they might listen.
  • haaljo
    haaljo Member Posts: 112
    JPF - ur new boiler?

    Any data on consumption before/after? u still commissioning?
  • jpf321
    jpf321 Member Posts: 1,568
    #3 ....

    would that be equal to 4 pieces of #2...nice...but a number 2.5 might be a better size equal to 2 pieces of #2...



    as a side question..does anyone have any history/clue as to how gortons got their number assignments
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • jpf321
    jpf321 Member Posts: 1,568
    thanks for the reminder

    I have data which I rash but didn't post..and new data collected but not processed...look for both shortly.
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • jpf321
    jpf321 Member Posts: 1,568
    edited January 2011
    deleted double post

    .
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    new products for gorton

    they should certainly make a bigger vent, however shorter in stature for those low headroom locations.......and....

    on this new model there should be a tell-tale showing when it has closed on steam arrival, as well as a temperature indicator showing the rising temperature. an option could also be a good low-pressure gauge to show the back-pressure during venting, so the optimum venting capacity can be more easily determined, for each dry return. 

    since you can never have too much venting, these will sell like hot cakes as well.--nbc
  • acl10
    acl10 Member Posts: 349
    NBC

    NBC I put a Gorton c on my dry return. I was wondering how venting a dry return one pipe steam effects the flow of condinsate into the boiler does the steam hold it back?
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    condensate return problems?

    main vents will aid the return of condensate, especially in wet-steam situations. the condensate is blown along by the escaping air. since the main vent is usually on the dry return, that's where the initial condensate will end up, ready to enter the wet return.

    if there are no main vents, and just a lot of high capacity radiator vents; then where would the condensate be blown towards, if not back into the radiator?

    you may be thinking of the effect of over-pressure, where the steam pressure pushes down on the boiler waterline, therefore raising the return waterline up 1.75 inches for each ounce of pressure. even at 12 ounces of pressure there is movement, and at 1.5 psi more so.--nbc
  • acl10
    acl10 Member Posts: 349
    NBC

    Thats what I meant. Will the steam pressure prevent the condinsate  from returning to the boiler. The vent is on the end of the dry return Where the pipe slopes into the wet return On the top just below the elbow of the downward pipe.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    effect of pressure on wet return

    no the pressure will not in general prevent the condensate from returning to the boiler. it is only the relative height difference between the wet return and the steaming boiler which is effected.  the steam pressure is pushing down on the boiler waterline, and therefore causing it to rise up in the return. at the end of steaming, the waterlines in both areas will fairly quickly return to equal. maybe with a gifford loop the effect would be different. i'll have to have a think about that!--nbc
  • acl10
    acl10 Member Posts: 349
    I put on a gorton D

     I put  a Gorton D on the return
  • Haviara
    Haviara Posts: 30
    Did you tap it right into the pipe

    or use new fittings?
  • TomM
    TomM Posts: 233
    whos got venture capital?

    i smell an investment opportunity.  :-)

    -

    There was an error rendering this rich post.

  • jpf321
    jpf321 Member Posts: 1,568
    just an update..

    I got the big order of gorton 2s yesterday. and then I promptly bought the house out of Ds ;-) as well.
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • Steamhead
    Steamhead Member Posts: 17,385
    edited January 2011
    "They said that because of this site there has been a huge surge in demand for the #2's.

    That's the power of The Wall!



    Makes me wonder what might have happened to Gorton if it weren't for us ;-) Some people say steam heat is dying, but how can that be true if they're seeing such increased demand?