Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

in7 with 2" header

jonny88
jonny88 Member Posts: 1,139
my company just installed a burnham in7.i got to the job during the installation.we used 2 2" risers coming out and then ran a 2"header.at the end of the header we used a full 2"tee but on the bull.the run of the tee went for both the equalizer and to pick up the 2 inch steam main.when i read the instruction manual it calls for a 3" header,which i pointed out.the reply was these books are written by engineers who dont know anything,i got 25 years doing this,dont try tell me my job.i read in dans book on steam never to bullhead a tee.im wondering what kind of call backs will we get.

Comments

  • Charlie from wmass
    Charlie from wmass Member Posts: 4,391
    Banging

    surging steam. Wet steam. or nothing at all as the home owns get told "It's Steam, Its noisy, What do you expect?" Wonder how they sized it? I should have you leave my card when you get done with that guy on jobs.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • jonny88
    jonny88 Member Posts: 1,139
    Only as good as your teacher

    Thanks for your reply Charlie.As for sizing the boiler my boss looked at the btus on old boiler and matched it to new one.this is why this site is so great.you realize a lot of what you learned is wrong.thanks for your help
This discussion has been closed.